UPS not found
  • UPS not found
145
Posted: ‎2021-07-08 01:06 AM . Last Modified: ‎2024-02-29 10:52 PM
1561
UPS not found
Hi all,
Last night i performed a firmware upgrade off  both the network management cards in our SMART RT 3000 ups (2x).
Although the firmware update went very smooth (i used the executable) i now have the problem that network management card can't find the ups anymore.
Both of the networkcards have the same problem. See screenshot
See the other screenshot about the versions.
I have tried to reseed the networkcard with the ups but no luck. I can access the webinterface with no problems but i cannot manage the ups anymore.
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander
It looks like you loaded the wrong firmware (your first screenshot says "Symmetra 3-Phase Application"). I'm pretty sure you want this file, which is the application for Smart-UPS and Matrix (hence the SUMX in the name) models. You can just go ahead and apply the whole update in the new package. After the card restarts, it should see your UPS.
Terry_Kennedy_apc
Commander
aah okay thanks!
I will let you know what the outcome is.
Posted: ‎2021-07-08 01:07 AM . Last Modified: ‎2024-02-29 10:52 PM
Thanks for the help! it is working again!