UPS Solution

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS Solution
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
RocknRollTim_apc
Crewman RocknRollTim_apc
Crewman

Posted: ‎2021-06-26 12:24 AM . Last Modified: ‎2024-03-19 02:55 AM

0 Likes
6
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:24 AM . Last Modified: ‎2024-03-19 02:55 AM

UPS Solution

Hi all,

I'm looking into a UPS solution for powering a BT Home Hub, BT Openreach Box and a Desktop PC with a monitor, the problem is I have these devices spread across the building so I may have to purchase 2 if needs be, I preferably would like the UPS(s) to be compact and small if possible, which model(s) of UPS do you recommend to achieve this solution? Your help and suggestions would be much appreciated.

Kind regards,

RocknRollTim

  

Labels
  • Labels:
  • General Questions & Suggestions
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RocknRollTim_apc
Crewman RocknRollTim_apc
Crewman

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:54 AM

0 Likes
0
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:54 AM

Hi voidstar,

You're right, the power extension lead is an extension cord, I'll ignore the extension cord when calculating the wattage needed. Thank you for your help also.

Regards,

RocknRollTim 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:55 AM

0 Likes
0
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:55 AM

Hello Tim, 

I am glad to hear you are interested in APC products, but before I can make any recommendations, I would have to know both the power requirements (wattage) of the equipment you are trying to power, as well as how much runtime (minutes) you are looking for in your UPS systems. 

Just to get you started, start looking at the BR series (like the BR1000G), it is our latest home end-user product line and has a very easy to use LCD screen. 

Thanks,
Shanon

Reply

Link copied. Please paste this link to share this article on your social media post.

RocknRollTim_apc
Crewman RocknRollTim_apc
Crewman

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:55 AM

0 Likes
0
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:55 AM

Hello Shanon,

Sorry for the delay in getting back to you, I have managed to find the wattage of each item I am wanting to power back up using UPSs and as follows: BT Home Hub (24 watts), Openreach Box (12 watts), Power Extension Lead (3250 watts) which both the BT Home Hub and Openreach Box are plugged into, PC (350 watts) and Monitor (360 watts). The BT Home Hub, Openreach Box and Power Extension Lead are in a separate room away from the PC and Monitor so I may need 2 UPSs, the only problem I see with this is the Power Extension Lead, do I think I have calculated this wrong? I used the following the website to calculate the number of watts for the Power Extension Lead.

Kind regards,

RocknRollTim

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:55 AM

0 Likes
0
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:55 AM

What is the Power Extension Lead? Is it a heater? Motor of some sort? I ask because that seems very high, the prices is in the thousands to support 3000W. If the total is nowhere near there, you might want to go with the BR700G, depending on what the actual load is.  

350W seems typical for a PC, but the monitor seems way too high, they are 40-80W typically. Either way, the BR1000G , BR1300G or BR1500G might be good fits for those, depending on the amount of runtime you want. 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:54 AM

0 Likes
0
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:54 AM

My guess is the "power extension lead" is an extension cord -- uses no power itself but, assuming UK voltages based on the BT equipment, can carry up to 13 Amps. If this is the case, we can ignore it for the purposes of calculating wattage needed.

Reply

Link copied. Please paste this link to share this article on your social media post.

RocknRollTim_apc
Crewman RocknRollTim_apc
Crewman

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:54 AM

0 Likes
0
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:54 AM

Hello Shanon,

The power extension lead is an extension lead like voidstar assumed. With regards to the BR700G I'll have a look at the specs to determine the actual load.

I agree the load for the monitor does seem way too high but I'll also have a look at the specs for the BR1000G, BR1300G and BR1500G.

Regards,

RocknRollTim  

Reply

Link copied. Please paste this link to share this article on your social media post.

RocknRollTim_apc
Crewman RocknRollTim_apc
Crewman

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:54 AM

0 Likes
0
1584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:25 AM . Last Modified: ‎2024-03-19 02:54 AM

Hi voidstar,

You're right, the power extension lead is an extension cord, I'll ignore the extension cord when calculating the wattage needed. Thank you for your help also.

Regards,

RocknRollTim 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore