UPS Shut Off During Power Failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS Shut Off During Power Failure
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
6
18151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

UPS Shut Off During Power Failure

We had a power failure today totaling about 30 seconds. I don't believe one of the UPSes stayed on during the failure. One of the servers connected to it said that it had been shutdown unexpectedly. The other one had some hard drive errors which we fixed by pulling the drive and doing a chkdsk.

I don't believe this UPS stayed up during the power failure. We have 3 UPSes and all have the AP9617 management card. A UPS that stayed up has the following in the log:

01/23/2009 08:12:42 UPS: No longer on battery power.
01/23/2009 08:12:08 UPS: On battery power in response to an input power problem.

The one that didn't stay on has the following:

01/23/2009 08:13:17 UPS: Restored the local network management interface-to-UPS communication.
01/23/2009 08:12:54 System: Network service started. System IP is from manually configured settings.
01/23/2009 08:12:54 System: Warmstart.

The unit is a SUA750RM2U. It only has about a 60% load. What can I do further to test this unit to figure out why it lost power in a short outage? Can I trust this device anymore? Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
18144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

i had a similar issue the other day where it turned out to be the battery.

during a self test, the unit runs on battery and compares the voltage drop to a table inside its microprocessor. if that voltage drop is normal, the self test passes. if not, the UPS illuminates the replace battery LED.

it sounds like the voltage drop is normal but the actual battery capacity is shot - meaning the runtime.

are you able to perform a self test on the battery with this load, does it do the same thing and drop the load after 5 seconds? (versus simulating a power outage?)

how old is this battery inside the UPS? based on what you find out, it just sounds like you need a new battery to me.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
18144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

I have a similar issue with a SmartUPS 10000XL

When there is a power failure or self test the power is never transferred out to the PDU's The Unit itself shows that all is well and passes the self test but the Step Down transformer is not showing that there is any load on the unit. The PDU's however show the amps being pulled. Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
18144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

a warmstart indicates the card did not lose power but did reboot. do you have any logs from powerchute network shutdown clients configured on this UPS?

i would suggest doing a pull plug test on the UPS with a non critical load so you can observe the behavior of the UPS to make sure it transfers to battery.

this just means to have a non critical load on the UPS, then pull the plug from AC power, and see if the UPS goes to battery.

if it does, then we can investigate further on your configuration. also, please confirm you have no other USB or serial cables attached to the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
18144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

The log from PCNS is:

01/23/2009 08:14:08 Communication has been established
01/23/2009 08:14:05 PowerChute Network Shutdown version 2.2.1 started
12/12/2008 23:20:02 Communication has been established
12/12/2008 23:19:22 PowerChute Network Shutdown version 2.2.1 started


There is nothing about loosing power or a indication of a shutdown.

Using event viewer (The system log) on the same system says:

The previous system shutdown at 8:11:05 AM on 1/23/2009 was unexpected.

For more information, see Help and Support Center at http://go.microsoft.com/fwlink/events.asp.

There are a bunch of entries after it about starting services as the machine booted again.








There are no USB or Serial cables attached the unit. Only power cables and a single network cable. I'll do the plug test this weekend on it and let you know the results. Thanks.

Jonathan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
18144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

I'm planning to do the pull test tonight. However last night I got a lot of emails from the unit saying:


01/24/2009 05:17:51 UPS: The battery is now installed.
01/24/2009 05:17:34 UPS: The battery is not installed properly.
01/24/2009 05:16:25 UPS: The battery is now installed.
01/24/2009 05:16:08 UPS: The battery is not installed properly.
01/24/2009 05:13:52 UPS: The battery is now installed.
01/24/2009 05:13:35 UPS: The battery is not installed properly.


Before I do the pull test I'll see if I can pull the battery out and double check to make sure it is connected well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
18144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

I ran the pull test with 3 computers without hard disks plugged to the UPS. 3 out of 5 of the green lights were lit for the load indicator.


Anyway, the unit completely shut off after about 5 seconds without power. No lights, no beeps, nothing.


I checked the voltage on the battery before I ran the test and it came out to 27.5V on the volt meter.


So my question is the battery bad or is the UPS bad?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
18145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

i had a similar issue the other day where it turned out to be the battery.

during a self test, the unit runs on battery and compares the voltage drop to a table inside its microprocessor. if that voltage drop is normal, the self test passes. if not, the UPS illuminates the replace battery LED.

it sounds like the voltage drop is normal but the actual battery capacity is shot - meaning the runtime.

are you able to perform a self test on the battery with this load, does it do the same thing and drop the load after 5 seconds? (versus simulating a power outage?)

how old is this battery inside the UPS? based on what you find out, it just sounds like you need a new battery to me.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of