Smart-UPS 1000 RM: Battery Installation Message

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1000 RM: Battery Installation Message
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
5
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

Smart-UPS 1000 RM: Battery Installation Message

I have a Smart-UPS 1000 RM at a facility with a network management card installed. On a fairly routine basis (every 7 days), the battery goes from an incorrectly installed state to a correctly installed state. I am guessing that this means the battery itself needs to be replaced but I wanted some other opinions before I make any hasty decisions.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • management
  • network_management_card
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:13 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
2065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:13 PM . Last Modified: ‎2024-03-15 01:24 AM

the battery replacement date should be indicated under the UPS tab->Configuration->General. If its never been replaced, it will match up with the manufacture date of the UPS which I believe is what you saw.

there is no SURE way to diagnose a unit versus battery in this situation i dont think. from my experience, i'd recommend a battery though since there is nothing else going on with the UPS that raises a red flag.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
2065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

inside your network management card, can you check and see what your self test schedule is set to? if its set to every 7 days, that means that this message is matching up with when the UPS is doing a self test.

it may also be helpful if you could paste some of the events in the log before and after this "battery not installed correctly" message as well. is it passing self tests? the battery should last 3-5 years so if its past that point, perhaps when the UPS is doing a self tests, it is causing this message when there is an extreme voltage drop during the self test.

i would suggest double checking what the battery voltage is reported as too through the interface.

these are good starting points that will hopefully lead us to the actual issue. they are mainly assumptions at this point though.

let me know what you find out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
2065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

The first time the issue started happening, on the 23rd of December, there was a scheduled self test that was supposed to happen but we did not get notification that occured. Instead on the 6th we got the first "UPS: The battery is not installed properly." Since the 6th the message has occurred at random intervals. The log, from what I can see, is simply filled with the "UPS: The battery is not installed properly," messages followed by "UPS: The Battery is now installed." It appears like I get 2 of the "UPS: The Battery is not installed properly" messages on the same day, one at 12:45pm (average time) and one at 1:30pm. Then the following day the "UPS: The battery is now installed" message comes across.

The self test is set to every 14 days.

Message was edited by: Khue

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
2065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

how old are the batteries? you can try to reseat them to see if it clears the message up. the batteries are hot swappable.

you could also try braindeading the UPS which will usually clear up any strange issues. I'd try this after you try a battery reseat ask this requires the UPS to be turned off.

to do this:

You need to power down all attached equipment and unplug it from the UPS. You then need to power down the UPS and unplug it from the utility power. Also, make sure that all communication cables are removed. Now, you want to hold down on the "off (o)" button until you hear an audible click (if not, proceed after 10 seconds anyway). Now, the internal circuitry of the UPS is reset, and you should be able to plug the UPS in, turn it on, attach all your equipment and power everything up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
2065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:12 PM . Last Modified: ‎2024-03-15 01:24 AM

Whats the most accurate way to retrieve the age of the battery? I have a couple different dates listed in the management application. I am not sure which one is the physical hardware and which one is the battery. Under UPS and the About section I see an 5/9/06.

By the way, thanks a bunch for the advice.

Edit: Self check took the entire unit offline. The router and the switched hooked up to the device took a dive. Probably means I should replace the battery. Is there any sort of indicator I can use to determine if it's just the battery that needs to be replaced or the entire unit?

Message was edited by: Khue

Message was edited by: Khue

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:13 PM . Last Modified: ‎2024-03-15 01:24 AM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:13 PM . Last Modified: ‎2024-03-15 01:24 AM

the battery replacement date should be indicated under the UPS tab->Configuration->General. If its never been replaced, it will match up with the manufacture date of the UPS which I believe is what you saw.

there is no SURE way to diagnose a unit versus battery in this situation i dont think. from my experience, i'd recommend a battery though since there is nothing else going on with the UPS that raises a red flag.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore