UPS SURTD3000XLT Hardware Fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS SURTD3000XLT Hardware Fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
4
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

UPS SURTD3000XLT Hardware Fault

We have a rack-mounted UPS, model number SURTD3000XLT.

We receive the following alarms, as viewed from the browser:
Inverter Fault
In Bypass: Hardware Fault

Viewing the Logs tab shows the following events:
UPS: In bypass in response to an internal hardware fault
UPS: An inverter fault exists


The event.txt file shows the following:
UPS: In bypass in response to an internal hardware fault. 0x011B
UPS: An inverter fault exists. 0x0165

The debug.txt file does not show any concurrent events.

The data.txt file (attached) shows the following readings that appear inconsistent with previous times:
Tups       T1ambF            
100.00     215.65             
100.00     215.46             
100.00     216.06             
100.00     216.37             
100.00     216.34             
100.00     215.40             
100.00     216.18             
100.00     216.37             
100.00     216.12             
100.00     216.37

The usual reading for Tups is about 68.
The usual reading for T1ambF is about 200

The front panel indicator LEDs are as follows:
    Bypass LED is amber
    Fault LED is red

When I press the test button the alarms clear but eventually return.

.

Additionally, the battery bled down to about 53% but is back up to 100% since the last test.

Two questions:

What do the column headers stand for, especially Tups & T1ambF?
Do I need to replace the UPS?

Thanks in advance.

Attachments
data.txt.zip
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

Hmm, thank you.

So that battery bar graph pattern you did show me, when did you see that? And I have to think that is exactly how it shows, top to bottom? Because you're right, that is not a pattern but typically the capacity goes from bottom to top. So, if it was showing battery capacity only and not a fault code, I'd expect:

0

0

1

1

1

Based on the event log and your serial number, I think the problem is likely with the UPS. I believe your unit would still be under factory warranty and be covered under that for a replacement if you contact technical support via phone or email with these log files and that serial number you gave to me.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

I think your data column headings are messed up or not aligned properly when viewing in the text file. 100% refers to battery capacity and to the right of that, 218 is likely the battery voltage which is normal.

TupsC or F is the internal temperature of the UPS and T1ambF refers to the ambient temperature probe #1 attached your Network Management card.

What I did is opened your data log in Notepad, put the cursor to the left of "Time" and tab it over to the right once. Or, use Excel to open it and it should align it properly.

I really need to see both the full event.txt and data.txt together but from what I can tell, the UPS is in bypass most recently and the battery charge and voltage is dropping.

It sounds like it is likely a UPS fault, but I'd want to know the serial number of the UPS if you have it and how old it is (which I can tell by the UPS serial number) because sometimes, faults can be due to faulty batteries but are not reported 100% clearly unfortunately.

Lastly, when the fault LED is illuminated along with bypass, does the battery bar graph (on the far right hand side that typically shows charge) display a particular pattern? This can tell us what the fault is directly from the UPS versus how the Network Management Interface is interpreting it.

It'd be something like

1

0

0

1

0

Where 1 means the LED is on and the 0 is LED is off.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

The battery bar graph does not display a particular pattern.  The LEDs were lit as if they were indicating a voltage level.

1

1

1

0

0

Serial #:    QS1233350191


I have attached the event  file.  Thank-you for your time.

Attachments
event.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

Hmm, thank you.

So that battery bar graph pattern you did show me, when did you see that? And I have to think that is exactly how it shows, top to bottom? Because you're right, that is not a pattern but typically the capacity goes from bottom to top. So, if it was showing battery capacity only and not a fault code, I'd expect:

0

0

1

1

1

Based on the event log and your serial number, I think the problem is likely with the UPS. I believe your unit would still be under factory warranty and be covered under that for a replacement if you contact technical support via phone or email with these log files and that serial number you gave to me.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

Thank-you Angela...I'll do that

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore