Smart-UPS 3000 discharge rate not matching runtime remaining

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 discharge rate not matching runtime remaining
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
5
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

Smart-UPS 3000 discharge rate not matching runtime remaining

Hi,

We have a Smart-UPS 3000 with typically a 15% load that started running on battery today.  It was on battery power for approximately 5 seconds, and in this time dropped to 90% capacity.

The UPS still shows a runtime remaining of 36 mins, but if it discharged at this rate then it would last less that a minute.

Is 5 seconds long enough to start calibrating the battery?  What was displaying the wrong value, the 90% capacity after 5 seconds, or the 36 min runtime?

Log:

07/14/2014    06:55:14    UPS: No longer on battery power.

07/14/2014    06:55:10    UPS: On battery power in response to distorted input.

07/14/2014    06:55:10    UPS: No longer compensating for a high input voltage.

07/14/2014    06:54:19    UPS: Compensating for a high input voltage.

07/14/2014    06:54:03    UPS: No longer on battery power.

07/14/2014    06:54:02    UPS: On battery power in response to distorted input.


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
roger_apc
Ensign roger_apc
Ensign

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

I deal with a large number of UPS units in locations across the US.  Over the past few months I have been dealing with some VERY old UPS units and also some VERY old batteries.  Some of the UPS units were installed in the mid to late 90"s and a few more in the early 2000's.  By far, the majority of our units are from 2006-2007.  Some of the batteries in those units have never been replaced.  We have started to run across units where the run time is listed at 30 min., but they fold after just a few seconds.  The older units don't seem to "self calibrate" very well.

Over the past few months I've tested and calibrated close to 50 UPS units, and here is what I've found.  Even with the short switch to battery power during a self-test, it's not uncommon for the battery % to drop 10-20%.  In this range, there doesn't seem to be any major change in runtime after doing a full runtime calibration.  In fact, some have shown an increase in runtime after calibration. But when that drop is in the 20-30%, the runtime will decrease dramatically.

I just ran a runtime calibration on a unit that was dropping to 69% on the self-test, and it was showing 66 min of runtime.  When I ran the calibration, it dropped to 38% within the first minute, and then ran for about 10 minutes before the calibration completed.  I think the calibration cuts off at around 20-25%.  So, as you can see, the discharge curve is no where close to linier.  NEXT MORNING:  The listed runtime has dropped to 26 minutes.

Just my experience.  YMMV

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

Hi,

The runtime is dependent on the age of the battery/s and the amount of times the battery has discharged / been in use. The UPS will calibrate when it switches to on battery. What is the exact model Smart-UPS 3000? How old is the battery/s and does the UPS switch to battery often?  With that information we can review the online runtime chat to see if the UPS is within specs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

What happens to the battery charge % readings in the first 5 to 30 or so seconds of when a UPS first goes to battery is not usually indicative of what will happen long term. Depending on load and battery age/health there is usually an initial drop in the first few seconds (that can sometimes be quite large),then sometimes what follows will be a short rebound (batt charge % & run time reported will increase very slightly/briefly), then it will drop steadily/slowly at a fairly even rate until low battery conditions are reached. All of this is governed by what has been termed the "coup de fouet" effect.

That there is sometimes a rebound is somewhat surprising to most people, and it comes in handy if you have a discharged (but not totally dead) car battery (eg left your lights on) if the battery can just crank the engine but not quite start it, turn everything off and wait about 5 to 10 mins then try again it may crank stronger and get the engine started.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

Thanks Bill, this battery was installed on January this year and looking at the logs this is the only time it's been running on battery other than it's initial calibration:

01/14/201406:26:16UPS: Runtime calibration passed via internal operation.
01/14/201406:01:02UPS: Started a runtime calibration.

How do I find the exact model?  SNMP just says:

.1.3.6.1.4.1.318.1.1.1.1.1.1.0 = STRING: "Smart-UPS 3000"

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:27 AM . Last Modified: ‎2024-03-12 03:02 AM

Back panel of the UPS should have a Model / Serial No Sticker.

Reply

Link copied. Please paste this link to share this article on your social media post.

roger_apc
Ensign roger_apc
Ensign

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

I deal with a large number of UPS units in locations across the US.  Over the past few months I have been dealing with some VERY old UPS units and also some VERY old batteries.  Some of the UPS units were installed in the mid to late 90"s and a few more in the early 2000's.  By far, the majority of our units are from 2006-2007.  Some of the batteries in those units have never been replaced.  We have started to run across units where the run time is listed at 30 min., but they fold after just a few seconds.  The older units don't seem to "self calibrate" very well.

Over the past few months I've tested and calibrated close to 50 UPS units, and here is what I've found.  Even with the short switch to battery power during a self-test, it's not uncommon for the battery % to drop 10-20%.  In this range, there doesn't seem to be any major change in runtime after doing a full runtime calibration.  In fact, some have shown an increase in runtime after calibration. But when that drop is in the 20-30%, the runtime will decrease dramatically.

I just ran a runtime calibration on a unit that was dropping to 69% on the self-test, and it was showing 66 min of runtime.  When I ran the calibration, it dropped to 38% within the first minute, and then ran for about 10 minutes before the calibration completed.  I think the calibration cuts off at around 20-25%.  So, as you can see, the discharge curve is no where close to linier.  NEXT MORNING:  The listed runtime has dropped to 26 minutes.

Just my experience.  YMMV

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of