SUA750I 'lost communication' emails

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA750I 'lost communication' emails
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
2
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

SUA750I 'lost communication' emails

We have an SUA750I. Which is protecting a Single Server and is connected via USB rather than serial.

We recently changed the Server. New Server, with Server 2012 R2 installed. Downloaded and installed the latest Powerchute software from the website. Now 3-4 times a day, Powerchute on the Server is emailing 'Communication Lost on Agent SERVER' status emails.

Upon logging on to the server and checking the logs, communication seems to be re-establishing instantly after the loss of communication. No manual intervention required.

This never happened on the old Server and we are using the exact same cable. Also tried a separate USB cable as a test and same thing.

I have read shutting down UPS and switching back on can fix, and also shutting server down and leaving off for a while can fix this - tried both no joy.

Also disabled the firewall on the Server as a test and no difference.

Any one had this before or offer any suggestions or troubleshooting steps??

Can't find the original Serial cable.

Steve

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 750
  • lost_comm
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

Hi,

Troubleshooting USB lost comm is difficult. You could use a USB analyzer like USBlyzer

Other option, purchase serial cable from APC.com SKU 940-0024 and use serial comm. NOTE: you must brain dead the UPS to switch from USB comm to serial comm. See Kbase FA156550

Uninstall PowerChute and install APCUPSD to see if APCUPSD also reports lost comm.

If you are using PBEServer and Console you can deselect e-mail notification via the console under Tools - Change Configuration Profile and uncheck Enable E-Mail

2420_pastedImage_0.png

Then open the PBEAgent web interface <https:// system ip address:6547> using Internet Explorer, Firefox, or Chrome and configure e-mails there.

To configure e-mail via the web interface go to Server Shutdown - System Settings

Then go to Events - Recipients and add recipients to receive the e-mails

Finally go to Events - Actions and select which events you want e-mails for.

By setting up e-mails via the web interface you will only get e-mails for the events you specify. When configuration e-mails via the Console - Server you get e-mails for all events. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

Hi,

Troubleshooting USB lost comm is difficult. You could use a USB analyzer like USBlyzer

Other option, purchase serial cable from APC.com SKU 940-0024 and use serial comm. NOTE: you must brain dead the UPS to switch from USB comm to serial comm. See Kbase FA156550

Uninstall PowerChute and install APCUPSD to see if APCUPSD also reports lost comm.

If you are using PBEServer and Console you can deselect e-mail notification via the console under Tools - Change Configuration Profile and uncheck Enable E-Mail

2420_pastedImage_0.png

Then open the PBEAgent web interface <https:// system ip address:6547> using Internet Explorer, Firefox, or Chrome and configure e-mails there.

To configure e-mail via the web interface go to Server Shutdown - System Settings

Then go to Events - Recipients and add recipients to receive the e-mails

Finally go to Events - Actions and select which events you want e-mails for.

By setting up e-mails via the web interface you will only get e-mails for the events you specify. When configuration e-mails via the Console - Server you get e-mails for all events. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:28 AM . Last Modified: ‎2024-03-12 03:02 AM

BillP,

Thanks for the quick response.

The serial cable was my next fix...we already have one somewhere but annoyingly I can't find it! We carried out some internal office moves at the start of the year and I made sure to put the serial cable in a safe place so that it wasn't thrown out...so safe a place I cannot find it. frown

I'll try disabling email in the profile as you mention and enabling on the agent.

Thanks,

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore