Two SMX1500RM2U lights flashing, won't power up, relay RY403, RY404 and RY405 clicking.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Two SMX1500RM2U lights flashing, won't power up, relay RY403, RY404 and RY405 clicking.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
4
794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

Two SMX1500RM2U lights flashing, won't power up, relay RY403, RY404 and RY405 clicking.

Both units were born in 2015 and died within months of each other.  Maybe the second one was missing the first one.

Anyone have an idea of what the relays are for and why they died so early?

Thanks,

Jeff

P.S. They didn't exhibit any signs of being sick prior to there death.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

Hi Jeff - 

Try disconnecting the internal battery and see if the unit will turn on. If it does, then you just need new batteries. Failed batteries can sometimes cause a unit to get stuck in a loop like this, and being from 2015 they are certainly due for replacement.

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

Counting up the number of SMX1500RM2U in use and considering how many are within a year of having the same birthday of the problem UPS above, is probably going to cause some of my teeth additional wear in the near future.  Sigh.

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

My records show both units as having 09.1 (ID20).

I have updated some of the other UPS's to 10.1.  It's a PIB to update them (having to power them off) and it's a bit scary thinking about the possibility of bricking the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

Unless APC recommends you update the firmware, either to correct a well-known problem or a specific issue you're having, I'd let them be if they are out of warranty. You'd be amazed how many motherboards come back with "problems" that were simply due to a bad BIOS flash.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 AM . Last Modified: ‎2024-03-15 06:03 AM

Hi Jeff - 

Try disconnecting the internal battery and see if the unit will turn on. If it does, then you just need new batteries. Failed batteries can sometimes cause a unit to get stuck in a loop like this, and being from 2015 they are certainly due for replacement.

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of