Hello everyone! I hope I am putting this in the correct forum.
One of our sites currently has 6 x SMX3000RMLV2U with the additional battery packs attached. For the last few months every time our property management company does a generator test we end up losing at least one of the main units. They do their tests really early in the morning so I finally decided to show up and this is what I observed. When they switched to generator we had a normal 10 second delay in the transfer and the units all held up fine. Hours later when they went to transfer off generator power the minute the power was cut to the apc units to wait for the three second transfer delay 3 of my APC units made a loud pop noise and the they went into a PFC Failure state. The other units went to battery power and 3 seconds later all the units except the ones that popped came back online. We had to reset the three units and then as a precaution I manually unplugged them to make sure they switched to battery and back and of course one unit failed so we replaced it. I am not sure where to start to check for the issue... This is getting out of hand as they are doing another test in July and we know we will lose another unit for sure. The property management said the units we have probably don't have a filter in them to handle the switch. That does not sound correct because the problem occurred as soon as the power was cut to make the transfer. They did not even get a chance to hang on for 3 seconds. Any pointers? Is this a configuration issue within the APC unit or is this an electrical issue?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
I have no plans to open the device up!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:04 AM
Hi Michael,
From your description of the issue it sounds like there may be some type of transient occurring during the switching process. I think the best bet is for you to contact your local tech support team and they can assist with reviewing logs and gathering configuration data. You can find your local contact info at support.apc.com
Thanks,
Liam
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:04 AM
Thanks, we opened a support ticket with APC but in the meantime if it helps any here is the logs...
04/13/2019 18:00:01 Device UPS: A site wiring fault no longer exists. 0x0236
04/13/2019 18:00:00 Device UPS: A site wiring fault exists. 0x0235
04/13/2019 18:00:00 Device UPS: A power factor correction input relay fault exists. 0x0150
04/13/2019 18:00:00 Device UPS: A battery bus soft start fault exists. 0x015B
04/13/2019 18:00:00 System DNS Network Error, Unknown socket/network error. 209 0x0032
04/13/2019 18:00:00 Device UPS: A power factor correction fault exists. 0x0161
04/13/2019 17:59:59 System DNS Network Error, Unknown socket/network error. 209 0x0032
04/13/2019 17:59:59 Device UPS: The output power is turned off. 0x0114
04/13/2019 17:59:59 Device UPS: The graceful shutdown period has ended. 0x014F
04/13/2019 17:59:58 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
04/13/2019 17:59:58 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
04/13/2019 17:59:58 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
04/13/2019 05:59:57 Device UPS: No longer on battery power. 0x010A
04/13/2019 05:59:24 Device UPS: On battery power in response to distorted input. 0x0109
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:04 AM
OK, so we definitely have indication of power issues here. Given the events the unit is reporting and the application, you may be able to improve your performance during the switch from generator power by disabling Green Mode on the UPS. In addition, you could try reducing the "Local Power Quality" setting to "Poor" (Assuming it's currently set to the default setting of "Good". )
Between these two setting changes it should reduce the effect of any damaging power events happening during the switch over.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
Both modes are set correct. Green mode is off and power quality is low. So I was watching the video closer of the issue and the APC units due indeed switch to battery for a split second and then go to PFC mode.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
Sorry do you mind telling me what PCB means?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
He's talking about Printed Circuit Boards. Please do not open the enclosure of the unit - there are no user serviceable parts inside the unit.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:08 AM . Last Modified: 2024-03-15 06:03 AM
I have no plans to open the device up!
Link copied. Please paste this link to share this article on your social media post.