SMX3000RMLV2U PFC Failure from Generator testing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX3000RMLV2U PFC Failure from Generator testing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:04 AM

0 Likes
8
3678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:04 AM

SMX3000RMLV2U PFC Failure from Generator testing

Hello everyone! I hope I am putting this in the correct forum. 

One of our sites currently has 6 x SMX3000RMLV2U with the additional battery packs attached. For the last few months every time our property management company does a generator test we end up losing at least one of the main units. They do their tests really early in the morning so I finally decided to show up and this is what I observed. When they switched to generator we had a normal 10 second delay in the transfer and the units all held up fine. Hours later when they went to transfer off generator power the minute the power was cut to the apc units to wait for the three second transfer delay 3 of my APC units made a loud pop noise and the they went into a PFC Failure state. The other units went to battery power and 3 seconds later all the units except the ones that popped came back online. We had to reset the three units and then as a precaution I manually unplugged them to make sure they switched to battery and back and of course one unit failed so we replaced it.  I am not sure where to start to check for the issue... This is getting out of hand as they are doing another test in July and we know we will lose another unit for sure. The property management said the units we have probably don't have a filter in them to handle the switch. That does not sound correct because the problem occurred as soon as the power was cut to make the transfer. They did not even get a chance to hang on for 3 seconds. Any pointers? Is this a configuration issue within the APC unit or is this an electrical issue? 

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
3677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

I have no plans to open the device up! 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:04 AM

0 Likes
0
3677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:04 AM

Hi Michael,

From your description of the issue it sounds like there may be some type of transient occurring during the switching process. I think the best bet is for you to contact your local tech support team and they can assist with reviewing logs and gathering configuration data. You can find your local contact info at support.apc.com

Thanks,

Liam 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:04 AM

0 Likes
0
3678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:04 AM

Thanks, we opened a support ticket with APC but in the meantime if it helps any here is the logs...

04/13/2019              18:00:01  Device     UPS: A site wiring fault no longer exists.      0x0236

04/13/2019              18:00:00  Device     UPS: A site wiring fault exists.    0x0235

04/13/2019              18:00:00  Device     UPS: A power factor correction input relay fault exists. 0x0150

04/13/2019              18:00:00  Device     UPS: A battery bus soft start fault exists.     0x015B

04/13/2019              18:00:00  System     DNS Network Error, Unknown socket/network error. 209             0x0032

04/13/2019              18:00:00  Device     UPS: A power factor correction fault exists. 0x0161

04/13/2019              17:59:59  System     DNS Network Error, Unknown socket/network error. 209             0x0032

04/13/2019              17:59:59  Device     UPS: The output power is turned off.          0x0114

04/13/2019              17:59:59  Device     UPS: The graceful shutdown period has ended.           0x014F

04/13/2019              17:59:58  Device     UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.             0x0135

04/13/2019              17:59:58  Device     UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.             0x0135

04/13/2019              17:59:58  Device     UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.             0x0135

04/13/2019              05:59:57  Device     UPS: No longer on battery power.              0x010A

04/13/2019              05:59:24  Device     UPS: On battery power in response to distorted input. 0x0109

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:04 AM

0 Likes
0
3678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:04 AM

OK, so we definitely have indication of power issues here. Given the events the unit is reporting and the application, you may be able to improve your performance during the switch from generator power by disabling Green Mode on the UPS. In addition, you could try reducing the "Local Power Quality" setting to "Poor" (Assuming it's currently set to the default setting of "Good". ) 

Between these two setting changes it should reduce the effect of any damaging power events happening during the switch over.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
3678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

Both modes are set correct. Green mode is off and power quality is low. So I was watching the video closer of the issue and the APC units due indeed switch to battery for a split second and then go to PFC mode. 

Reply

Link copied. Please paste this link to share this article on your social media post.

older_apc
Crewman older_apc
Crewman

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
3678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

Hi Michael,
Please tell me the model of the PCB if possible.
Thank.
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
3678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

Sorry do you mind telling me what PCB means?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
3678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

He's talking about Printed Circuit Boards. Please do not open the enclosure of the unit - there are no user serviceable parts inside the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

0 Likes
0
3678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 AM . Last Modified: ‎2024-03-15 06:03 AM

I have no plans to open the device up! 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of