Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Testing 1500 VA Battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Testing 1500 VA Battery
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
pcerna_apc
pcerna_apc
Cadet

Posted: ‎2021-07-28 11:33 PM

0 Likes
5
1656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-28 11:33 PM

Testing 1500 VA Battery

This was originally posted on APC forums on 10/26/2009


We would like to use a amp/hr tester on our 1500 VA batteries. What type/brand of battery tester should we use?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-07-28 11:34 PM

0 Likes
0
1656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-28 11:34 PM

This was originally posted on APC forums on 11/12/2009


You could always charge the unit up to 100%, pull it out of the unit, attach a 5A load and measure how fast the voltage drops. If it doesn't drop from 24V too fast, you're in good shape. If all of a sudden it drops to 16V and then to 12V, you know your battery can't handle a load. I have to say that I agree with the other users in this thread, you don't really need to perform this kind of testing on the UPS. The 1500VA is pretty good at moderating itself and determining the life time of the battery. It aint perfect, but it works and saves a lot of labor hours.

See Answer In Context

Reply
Replies 5
Techie_apc
Admiral Techie_apc
Admiral

Posted: ‎2021-07-28 11:33 PM

0 Likes
0
1656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-28 11:33 PM

This was originally posted on APC forums on 10/29/2009


Patty,

I do not think that there is a need for separate battery tester to check the UPS batteries condition. The Replace battery indicator is lit whenever the automatic diagnostic test has determined the battery is near the end of its useful life. It is a warning that the battery needs to be replaced within 4 weeks. APC Smart UPS performs a self test at start up and every 14 days automatically in order to warn the Customer if the battery needs replacement.

Reply
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-07-28 11:33 PM

0 Likes
0
1656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-28 11:33 PM

This was originally posted on APC forums on 10/26/2009


The best way to determine a batteries status is to check its internal impedance under load. To do this the best meter you can use is an Alber Cellcorder.

http://www.alber.com/ProdPageCellcorderCRT300.htm

However this meter will cost more than 10 of the UPS's that you are checking the batteries on. If you think your batteries are bad disconnect your computer load and hook a lamp up with a 100W bulb. Open the supply circuit breaker that feeds the outlet the UPS is in and measure how long the battery run time is.

Go to the APC website and and perform a runtime calculator on the model UPS you have and see if your UPS is performing with ~25% of what its supposed to be. If not the battery is getting old and needs to be replaced.

Just a note on a common practice I see recommened is to just unplug the UPS from the wall to test it. This is not safe to do. When you unplug the UPS from the wall you remove the ground from the UPS and from the supplied load. Always open the supply breaker if you want to do a battery discharge test.

Reply
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-07-28 11:33 PM

0 Likes
0
1656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-28 11:33 PM

This was originally posted on APC forums on 10/26/2009


Our APC units already have a self test function in place that will determine the total health of your UPS' battery. If this is insufficient enough for "data" gathering, APC cannot make a recommendation on third party testing solutions. Perhaps another customer on the forums can give more input?

Reply
HDRW_apc
Crewman HDRW_apc
Crewman

Posted: ‎2021-07-28 11:34 PM

0 Likes
0
1656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-28 11:34 PM

This was originally posted on APC forums on 10/29/2009


I have a West Mountain Radio Computer Battery Tester II (CBA II) which I've used to test VRLA batteries, but not APC ones.

It connects to the USB port of a PC onto which you load their software, and once it's up and running you connect it to the battery, and set the parameters to match the battery. I always find it suggests a larger discharge current than I like, so I wind that down to something like C/10 (so about 1.5A for a 17Ah battery). It then draws that current and measures the voltage across the battery, and plots a graph of it until it reaches the shut-down voltage you've set, when you can read the number of Amp-hours it's achieved. (Charge it up again straight away - shouldn't leave Lead-Acid batteries discharged!)

Since some batteries are rated at C/20, you almost never get the rated capacity when testing at C/10! But it gives you an idea of the health of the battery.

They cost about US$120, and googling for "CBA II" will find where to get them, although I like Impulse Electronics in California.

They come with "PowerPole" connectors for the battery, so you may want to get some of these at the same time, to make up your own leads for connecting the battery.

I have no connection with West Mountain Radio or Impulse Electronics, other than being a happy customer!

Hope this helps...

Cheers, Howard

Reply
MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-07-28 11:34 PM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-28 11:34 PM

This was originally posted on APC forums on 11/12/2009


You could always charge the unit up to 100%, pull it out of the unit, attach a 5A load and measure how fast the voltage drops. If it doesn't drop from 24V too fast, you're in good shape. If all of a sudden it drops to 16V and then to 12V, you know your battery can't handle a load. I have to say that I agree with the other users in this thread, you don't really need to perform this kind of testing on the UPS. The 1500VA is pretty good at moderating itself and determining the life time of the battery. It aint perfect, but it works and saves a lot of labor hours.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc