Can we use a SURT 8000XLT in a 240/415 50hz building

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can we use a SURT 8000XLT in a 240/415 50hz building
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
RangerBob_apc
RangerBob_apc
Cadet

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-02-14 02:35 AM

0 Likes
3
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-02-14 02:35 AM

Can we use a SURT 8000XLT in a 240/415 50hz building

I need a definitive answer to this. A contractor has installed several SURT 8000XLT in cabinets located in buildings that are powered by 240/425 50 hz. They are not wired up yet. When I look at the specs of this UPS, I am led to think that it is designed for North America and should be on a split phase 120/208 circuit. Before I tell the contractor that he screwed up and should have bought SURT8000RMXLI units, I want to make sure that there is no way of using the SURT 8000XLT units in this setup. If there is a way to wire them up using single phase 240VAC power, please let me know. Thank you very much.

RangerBob

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-01-31 02:55 AM

well by design SURT8000XLT is designed for NAM which is generally the H, H, G but since these systems are similar, the H, N, G is ok because as long as it gets 240, it doesnt really care. but yes, the output would be an issue i guess for your particular equipment because you cannot have it output the neutral, just the H, H, G. my understanding would be that there is no change to the capacity in kVA since the voltage is the same.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-01-31 02:55 AM

i asked our SURT expert here and got an answer.

as long as it is 240 H, N, G, the UPS should work. you will need to program the output to 240v though since the default is 208v. it will auto-sense 50Hz but if you coldstart thte unit off of its battery with no AC input, it works at 60Hz.

this UPS always outputs two hot legs that if you measure across them will be 240v but measuring each leg along will not be balanced - i.e. maybe 130v and 110v or similar. so you cant wire them to a 120v panel for instance. then you will have your ground connection as well in the output.

if you put the unit into bypass though, just watch out since i am not sure what you are attaching to this since it will pass through utility power to the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

RangerBob_apc
RangerBob_apc
Cadet

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
0
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-02-14 02:33 AM

OK that is a "no" answer. It is possible to use one 240 phase, but the output would not be something I would risk mission critical equipment on. Would the output power also be only half or 4KVA? I'm telling them tomorrow to order the correct equipment. PS the wiring indicates 3 wires hot / hot and ground, no neutral.

Message was edited by: RangerBob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
1428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 11:34 PM . Last Modified: ‎2024-01-31 02:55 AM

well by design SURT8000XLT is designed for NAM which is generally the H, H, G but since these systems are similar, the H, N, G is ok because as long as it gets 240, it doesnt really care. but yes, the output would be an issue i guess for your particular equipment because you cannot have it output the neutral, just the H, H, G. my understanding would be that there is no change to the capacity in kVA since the voltage is the same.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore