Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 11:25 PM . Last Modified: 2024-03-06 03:12 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:25 PM . Last Modified: 2024-03-06 03:12 AM
There is a temprature sensor connected to my AP9619 NMC card and I am configuring the temperature thresholds. When configuring the APC Network Shutdown software I noticed there is a configuration I can set called "Environment:Temparature Probe 1 out of range". There is also a "Probe 2" version of this. Will the network shutdown software identify my temperature sensor as Probe 1?
The thresholds are defined as High to Max and Low to Min. If the temperature increases will the network shutdown software identify an "Out of Range" when it hits a High or Maximum threshold? Based on the answer this will determine the values I set for the thresholds.
Thanks for your help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:25 PM . Last Modified: 2024-03-06 03:12 AM
no problem.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:25 PM . Last Modified: 2024-03-06 03:12 AM
hi
yes, you only have one probe on the AP9619 so it should be probe 1. PCNS will initiate a shutdown based on ANY temperature violation (or out of range value). unfortunately, you cannot specify for it to do nothing on a high alert, and then shutdown on a maximum alert. if so, you'd have to disable the high alert completely on the NMC interface from alerting you.
hope that helps.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:25 PM . Last Modified: 2024-03-06 03:12 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:25 PM . Last Modified: 2024-03-06 03:12 AM
I appreciate your help! This answers my question. Thank you. 😃
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:25 PM . Last Modified: 2024-03-06 03:12 AM
no problem.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.