T Sensor Error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • T Sensor Error
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:51 AM . Last Modified: ‎2024-03-17 11:47 PM

0 Likes
4
2628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 AM . Last Modified: ‎2024-03-17 11:47 PM

T Sensor Error

I have this error on an APC. 9631 mgmt card is installed. Not sure what the error even means or how to clear it. Any help would be greatly appreciated. 

Environment: A maximum temperature threshold violation exists for integrated Environmental Monitor T Sensor (NA at NA) reporting over 0.0 C

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
2628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Thank you for the help. I changed to Fahrenheit and then changed the thresholds and that resolved my issues.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:51 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
2628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 AM . Last Modified: ‎2024-03-17 11:46 PM

Hi Jonathan,

The AP9631 Network Management Card is like a NIC for your UPS. It supports accessories that plug into Universal I/O (UIO) ports. An included accessory is an AP9335T temperature sensor that you typically install/route somewhere in the rack where your UPS is so you can see the ambient/environmental temperature in the area. 

The message looks to me telling you that there is a maximum temperature violation. Which, as part of using the temperature sensor, you can set high/low and min/max thresholds for temperature values which you can be alarmed on through multiple methods if you so choose (email, syslog, SNMP, etc). Though the message looks a little odd with the NA and 0.0ºC. NA can be programmed in by someone but the temp reading is strange.

The easiest thing to do is to log into the AP9631 and see what is being reported for temperature and what is set for threshold configurations. Then, also check the logs and see what is going on there.

If you are on newer 6.X firmware, try going to the status menu->Universal I/O menu and then check the configuration stuff under Configuration->Universal I/O and let us know what you find. Any screenshots would be good.

Also, you can share any logs if you want by downloading the .tar file, explained here on how to download it -http://www.apc.com/us/en/faqs/FA156131 from About->Support menu or through other methods.

For reference, you should see stuff like this in the web interface so if you're not, we'll have to see what is happening:

HKiRUNkCDfdlKwyOIv3YZg%3D%3D.pngHKiRUNkCDfdlKwyOIv3YZg%3D%3D.png

rSEe9ZYUvRtiPBOiuZCAnA%3D%3D.pngrSEe9ZYUvRtiPBOiuZCAnA%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
2628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Here is a screenshot of that I/O status. What's funny is everything is in Celsius and not Fahrenheit. Can this be changed?

it84J%2B%2BHu8zr7%2BsLGvNuzw%3D%3D.pngit84J%2B%2BHu8zr7%2BsLGvNuzw%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
2628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Yes, it goes on a by-user basis. For the user you're logged in as, look for your username on the top right of the screen. Click on it and it will give you a shortcut to the user's preference and you can change it to US Customary there.

So it seems like these are legit trying to notify you (correctly) because all of the thresholds are 0's and the actual temp is higher than that.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
2629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Thank you for the help. I changed to Fahrenheit and then changed the thresholds and that resolved my issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of