New SRT 2200 - "Battery pack 1, cartridge 2 is not installed"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • New SRT 2200 - "Battery pack 1, cartridge 2 is not installed"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
6
6287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

New SRT 2200 - "Battery pack 1, cartridge 2 is not installed"

Hello, we have a new Smart-UPS SRT 2200 installed.  The Home screen is reporting a Critical Alarm - Battery pack 1, cartridge 2 is not installed."

The Battery System Status screen says "Battery Pack 1 - Health OK, Status Critical".

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
6274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Hi Brannen,

The battery voltage looks ok, but I would expect the state of charge to be higher (if the unit was connected to AC input previously, and unless there were self tests, run time calibrations, or run time tests with no AC performed before capturing the status). Run time calibration can only be performed at 100% battery charge, this is the reason why the unit refused the calibration. The Battery Replacement Date seems offset as well.

The external battery pack has two internal battery modules, counted as Battery Pack 1, Cartridge 1 and Cartridge 2. 

At this stage, it would be best to contact your local APC Tech Support for further troubleshooting - including a UPS firmware upgrade, considering the unusual Battery Replacement Date.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
6274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Hi Brannen,

SRT UPS models require some amount of load for battery recognition to work properly - can you try to clear the alarm, connect at least 400W load, then perform a self-test?

If your usual load is, or exceeds 400W, then the next thing I can think of is that the Battery Install Dates may not be set appropriately. The installation dates can be set manually on the UPS display interface in Configuration Menu - Battery - Install Date menu. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
6274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Dear Szabi,

How can I change the date, after the installation and commissioning of the equipment? We did the test with the given instruction, but it does not allow me to change the date. Will there be a special way or condition to save the changes?

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
6274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Hi Carlos,

Active battery related alerts may prevent saving changes made to the Battery Install Date. Clearing the alert on the UPS display interface should restore the unit to normal operation, at least for a while. Once there are no active alerts (the display interface is blue rather than amber or red) you should be able to save changes made to Battery Install Date. Let me know how it goes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
6274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Thanks for your reply.  

I'm trying to change the date.

Before I change, this is what's shown on UPS status, on a brand new battery:

Battery Status
State of Charge
49.0 %
Battery Voltage
82.1  VDC
Next Battery Replacement Date
01/01/2000
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
6274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

I'm remote from the device.  Can I change it through the webpage?  I don't see where.

I was able to run a self test.

However I'm not able to calibrate:

Calibration Refused 09/13/2018 management device

state of charge not acceptable

I found where to change the battery date, and I did for Battery Cartridge 1.  But It's not letting me change the installation date for Battery Cartridge 2, it says it's disconnected.

What is cartridge 2? The external battery pack?

Battery system status shows:  internal pack, health ok, status ok.

Battery pack 1, health ok, status critical.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

0 Likes
0
6275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:52 AM . Last Modified: ‎2024-03-17 11:46 PM

Hi Brannen,

The battery voltage looks ok, but I would expect the state of charge to be higher (if the unit was connected to AC input previously, and unless there were self tests, run time calibrations, or run time tests with no AC performed before capturing the status). Run time calibration can only be performed at 100% battery charge, this is the reason why the unit refused the calibration. The Battery Replacement Date seems offset as well.

The external battery pack has two internal battery modules, counted as Battery Pack 1, Cartridge 1 and Cartridge 2. 

At this stage, it would be best to contact your local APC Tech Support for further troubleshooting - including a UPS firmware upgrade, considering the unusual Battery Replacement Date.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore