Symmetra LX. Can it run on one MIM?
  • Symmetra LX. Can it run on one MIM?
Posted: ‎2021-06-28 11:13 PM . Last Modified: ‎2024-03-14 03:02 AM
1021
Have a Symmetra LX 16PXR with one bad MIM. Can I run the load with one MIM for the time being?
Replies 4
Erasmus_apc
Sisko Erasmus_apc
Sisko
Yes, the SYLX can be fully functional with only one intelligence module installed. You will have no redundancy if that one fails, of course.
Erasmus_apc
Sisko Erasmus_apc
Sisko
To switch any states safely using an SBP switch, the UPS itself should be in maintenance bypass (using the maintenance bypass switch in the top right of the inside of the UPS, under the front cover). Once the UPS is confirmed to be in maintenance bypass, you can then switch the SBP setting from Test to Normal. Once this is done successfully, you can then take the UPS itself out of maintenance bypass.
Thank you for all your help.