PCNS Config --> Probably a really simple question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS Config --> Probably a really simple question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-28 11:12 PM . Last Modified: ‎2024-03-14 03:02 AM

0 Likes
5
2934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:12 PM . Last Modified: ‎2024-03-14 03:02 AM

PCNS Config --> Probably a really simple question

So, I've got about 20 servers that I've install PCNS on (Windows & Linux) but I have also registered all of their IP's on the Symmetra 40K management card.

I've done some searching and I have found tons of stuff on configuring PCNS, but I guess I'm wondering if I even have to configure the events in the servers GUI???

With PCNS installed and adding their IP's to be shutdown from the management card will the UPS signal out to all clients and gracefully shut them down without configuring each and every event on the server?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-28 11:13 PM . Last Modified: ‎2024-03-14 03:02 AM

0 Likes
0
2934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:13 PM . Last Modified: ‎2024-03-14 03:02 AM

I didn't get an answer to the DNS issue, but the original question was answered.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:12 PM . Last Modified: ‎2024-03-14 03:02 AM

0 Likes
0
2934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:12 PM . Last Modified: ‎2024-03-14 03:02 AM

If you leave PCNS totally unconfigured on each of your servers, then by default they will only shut down the servers when the UPS' "Low Battery Signal Duration" is reached. This function is hard coded and unable to be changed. This setting can be found in the GUI of the Network Card under the UPS settings tab. It generally ranges from 2m to 20m.

Reply

Link copied. Please paste this link to share this article on your social media post.

Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-28 11:12 PM . Last Modified: ‎2024-03-14 03:02 AM

0 Likes
0
2934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:12 PM . Last Modified: ‎2024-03-14 03:02 AM

Awesome! That's what I figured. Thanks for the super fast response.

We had power go out over the weekend and 4 servers that didn't have the configs shutdown gracefully, but the ones I configured (with the help of an APC tech over the phone) just died when power was depleted. So, in the interest of ease I'm probably just going to leave them unconfigured since it's only about 20.

I do have one other question though. From the UPS logs I saw this error:
11/15/2009 15:01:09 System: Email: Could not resolve 'mail.dwr.com'.

And I don't really know why because in the past it's worked fine and this is the first time I've seen this error on it when power has gone out. There haven't been any system changes and the mail server was up because it's in a whole other state.

Thanks again

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:13 PM . Last Modified: ‎2024-03-14 03:02 AM

0 Likes
0
2934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:13 PM . Last Modified: ‎2024-03-14 03:02 AM

Sorry about the delay, it is difficult to keep track of all the posts sometimes. I would recommend doublechecking your DNS settings and TCP/IP settings fully and make sure they sync against what your network would require for perfect comm to your DNS server. If you are using an external DNS (OpenDNS, etc?) this can cause common communication issues. How often does this come up, if it is even doing it since your last response? This can sometimes be a traffic issue, but I would also check to make sure the mail address you have specified comes up as your primary using NSLOOKUP in the command prompt. Technically, the one you specify should have the lowest "mx" value when you do a lookup using the "mx" type of query.

Reply

Link copied. Please paste this link to share this article on your social media post.

Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-28 11:13 PM . Last Modified: ‎2024-03-14 03:02 AM

0 Likes
0
2934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:13 PM . Last Modified: ‎2024-03-14 03:02 AM

No worries. I verified all the IP/DNS settings and everything is good there for sure.

I actually think this may be due to the UPS killing power to my router or a switch, but I don't know why. I'm planning on running a test today after hours so I can watch.

It used to be OK and didn't shut the router off before. The only change was that I unregistered my Catalyst 4507's IP from the NMC because I was told it unnecessary to have it in there.

Maybe you can answer this last one easily before I search and post it. I want to test the PowerChute Shutdown command, but if it doesn't work on some servers I don't want them to go down hard.

Would my best option be to log into the NMC and go to Control>Initiate a UPS Control Action>Put UPS in Bypass and check "Send PowerChute Server Shutdown"? I just want to verify that all servers are receiving the command and actually shutdown gracefully. If so, then I'll do a full power failure test.

Reply

Link copied. Please paste this link to share this article on your social media post.

Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-28 11:13 PM . Last Modified: ‎2024-03-14 03:02 AM

0 Likes
0
2935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:13 PM . Last Modified: ‎2024-03-14 03:02 AM

I didn't get an answer to the DNS issue, but the original question was answered.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore