Smart-UPS3000 AP9631 SNMP card

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS3000 AP9631 SNMP card
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:52 PM . Last Modified: ‎2024-03-06 10:34 PM

0 Likes
2
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:52 PM . Last Modified: ‎2024-03-06 10:34 PM

Smart-UPS3000 AP9631 SNMP card

Hi,

Need help to answer the below questions.

1. Where can download the AP9631 SNMP card event alert list?

2. How to filter the "Bypass not in range, high voltage" from the email notification?

3. Bypass not in range, high voltage is critical alert, when back to normal the alert is An input voltage of frequency problem no longer prevent switch to bypass mode?

4. what is the meaning of "On battery power in response rapid change of input"?

5. What is the meaning of "On bttery power is response to distorted input"?

Thanks.

Regards,

Yong

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:52 PM . Last Modified: ‎2024-03-06 10:34 PM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:52 PM . Last Modified: ‎2024-03-06 10:34 PM

Hi Michael,

Thanks for the information.

I can't found the event alert details in the MIB file, I need to know all the event alert meaning so I can explain to client when they receive the alert.

After filter critical alert "Bypass not in range, high voltage" do I need to filter the clear alert " An input voltage of frequency problem no longer prevent switch to bypass mode"? as I know both message will trigger when critical and clear.

I can't found the bypass out of range from the event action.

I would like to know if power failure what kind of event alert will trigger?

Below are the SNMP card I'm using

UPS Network Management 2

Smart-UPSMatrix Application

Thanks.

Regards,

Yong

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:52 PM . Last Modified: ‎2024-03-06 10:34 PM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:52 PM . Last Modified: ‎2024-03-06 10:34 PM

Hi Yow,

On 12/16/2015 6:48 PM, yow said:

1. Where can download the AP9631 SNMP card event alert list?

the event list will depend on the ups it is connected to. You can download the MIb at the following link. http://www.apc.com/site/support/us/en/faq/?page=content&country=ITB〈=en&locale=en_US&id=FA156048&redirect=true

On 12/16/2015 6:48 PM, yow said:

2. How to filter the "Bypass not in range, high voltage" from the email notification?

log into the NMc then proceed to this tree: configuration -> notificaiton -> event actions -> by event -> bypass -> bypass out of range. You can then select the email recipient you want to disable notification for. It will only do it was the event you select.

On 12/16/2015 6:48 PM, yow said:

3. Bypass not in range, high voltage is critical alert, when back to normal the alert is An input voltage of frequency problem no longer prevent switch to bypass mode?

 yes that should be the clearing event you see. 

On 12/16/2015 6:48 PM, yow said:

4. what is the meaning of "On battery power in response rapid change of input"?

this means the ups went onto battery because the input power changed in a quick matter that the ups did not like. We can look at the data logs to possible see why. So for example it could be we had 208 volts and then had a sudden spike up to 230 volts or something along those lines. 

On 12/16/2015 6:48 PM, yow said:

5. What is the meaning of "On bttery power is response to distorted input"?

this means the UPS went to battery mode due to the sine wave input being distorted. Sometimes called "dirty power" 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:52 PM . Last Modified: ‎2024-03-06 10:34 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:52 PM . Last Modified: ‎2024-03-06 10:34 PM

Hi Michael,

Thanks for the information.

I can't found the event alert details in the MIB file, I need to know all the event alert meaning so I can explain to client when they receive the alert.

After filter critical alert "Bypass not in range, high voltage" do I need to filter the clear alert " An input voltage of frequency problem no longer prevent switch to bypass mode"? as I know both message will trigger when critical and clear.

I can't found the bypass out of range from the event action.

I would like to know if power failure what kind of event alert will trigger?

Below are the SNMP card I'm using

UPS Network Management 2

Smart-UPSMatrix Application

Thanks.

Regards,

Yong

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of