Smart UPS X3000 "A power factor correction fault exists"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS X3000 "A power factor correction fault exists"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

0 Likes
4
11116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

Smart UPS X3000 "A power factor correction fault exists"

Note: Just updated the UPS Serial number.  I listed the wrong one at first.

another UPS problem over the weekend that I have questions about.

We had an UPS go down this weekend and shut its outputs off.

The UPS is showing an error of "A power factor correction fault exists [0x0161].

Its a SMX3000RMLV2UNC (SN: AS1532134742) with network card (AP9631)

Why would the UPS turn its outputs off and not switch to the batteries?

I have seen this asked in older discussions.  It seems to be something that may require the UPS to be replaced, I just don't understand if its caused by internal parts going bad or external power surges killing the UPS and then why doesn't it at least switch to batteries.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

0 Likes
0
11110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

Thanks for the logs. 

Do any of the attached loads have dual power inputs? If so, are they both connected to the UPS? Any other details you can provide about the load? (Makes/Models...)

Have you tried performing a "brain dead", and if so - did it clear the fault?

To perform a "Brain Dead" you would want to turn off the UPS and remove the connected load. Then unplug the UPS from input power and disconnect the internal battery. Wait a moment and plug the unit back in and turn it back on. If the fault clears and the UPS turns back on without issue, then it was likely an error and not a true hardware failure.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

0 Likes
0
11110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

Our UPS is connected to a single APC AC distribution unit (AP7902) that has all the equipment connected to it.

Looking at one of our other sites with the same equipment configuration, the UPS is running a load current of 2.2 Amps, Output VA 9.7% and output Watts of 9.3%.

We have two external batteries attached to each UPS.

Our technician will be returning to site in a day or two with a replacement UPS. This one will be brought back to the warehouse for troubleshooting and possible repair.

I can have him do a "brain dead" before he removes it from system to see if that clears the fault or not.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

0 Likes
0
11110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

Hi Charles - 

A Power Factor Correction Fault would indicate a hardware fault on the output side of the UPS. If the UPS has a hardware fault it may not have the capacity to switch to battery as expected.

Do you have a Network Management Card in this UPS? If so, can you provide the logs? (From the Web interface go to "About", then "Support". From there you can generate and download the logs.)

It would also be helpful to know exactly what is connected to the UPS for load. Some of this might be easier to do by calling in to our tech support teams directly. You can find your local support at http://support.apcc.com

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

0 Likes
0
11110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

As mentioned above it does have a network card.

The logs are attached. IP addresses have been "x"ed out.

The UPS is still on network and powered up running on its batteries but disconnected from main power. So the data logs do not show much in them.

The load on the UPS is IT gear and a few VHF radio systems.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

0 Likes
0
11111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

Thanks for the logs. 

Do any of the attached loads have dual power inputs? If so, are they both connected to the UPS? Any other details you can provide about the load? (Makes/Models...)

Have you tried performing a "brain dead", and if so - did it clear the fault?

To perform a "Brain Dead" you would want to turn off the UPS and remove the connected load. Then unplug the UPS from input power and disconnect the internal battery. Wait a moment and plug the unit back in and turn it back on. If the fault clears and the UPS turns back on without issue, then it was likely an error and not a true hardware failure.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

0 Likes
0
11111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-18 12:19 AM

Our UPS is connected to a single APC AC distribution unit (AP7902) that has all the equipment connected to it.

Looking at one of our other sites with the same equipment configuration, the UPS is running a load current of 2.2 Amps, Output VA 9.7% and output Watts of 9.3%.

We have two external batteries attached to each UPS.

Our technician will be returning to site in a day or two with a replacement UPS. This one will be brought back to the warehouse for troubleshooting and possible repair.

I can have him do a "brain dead" before he removes it from system to see if that clears the fault or not.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore