Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:06 AM
I'm getting this Alarms SENSOR TYPE: Battery Temperature | SENSOR TYPE: Temp | Value Too High - 95.0 F. I check the UPS and see this is for the Internal Temperature not the Universal I/O Temp Sensor I have connected on port 1.
My question is: Can the threshold of the internal temperature alarm trigger be change? or is this a factory setting that cannot be change?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:06 AM
Thanks Angela again - I checked my logs earlier and it seems that we have had this problem for a while now. Im contacting support to see if they recommend a battery change or something else.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:06 AM
Hi Pavel,
Yes, this is a factory setting. UPS Internal Temperature threshold is specific to the UPS model/type and I don't know of a UPS that we offer that actually allows you to change it.
Thus, I suggest you investigate if there is a hot battery or other issue with this UPS as soon as possible to avoid other problems.
Does the ambient temperature probe near the UPS read hot too, which could maybe indicate there is another problem in the area?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:06 AM
Thanks for the clarification Angela
The ambient temp the probe near the UPS is reading at 77F. Right now the Batt Temp went down to 89F
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:06 AM
Oh ok. I'd definitely keep an eye on it to make sure there is not a problem with the battery or something like that. I would expect something a little bit closer to 70-80ºF. You could also check the data log to see what TupsF (internal temp of the UPS) column shows over time and see if it has steadily climbed and when it started.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:06 AM
Thanks Angela again - I checked my logs earlier and it seems that we have had this problem for a while now. Im contacting support to see if they recommend a battery change or something else.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of