Replaced Battery and Smart UPS 1500 won't turn on

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Replaced Battery and Smart UPS 1500 won't turn on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
10
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

Replaced Battery and Smart UPS 1500 won't turn on

Hi,

I have an APC  Smart-UPS 1500 - Model; SUA1500I (http://www.apc.com/resource/include/techspec_index.cfm?base_sku=sua1500i&tab=models).  The battery required replacement and I've just replaced it with the recommend battery RBC7  (http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=RBC7&tab=models). The replacement of the battery was very straight forward with help of the user manual. Since the battery has been replaced, the UPS will not turn on and I'm unsure why this is.

 I thought the  Overload Protector may have tripped because it seems to stick out about 5 mm but from looking at the forum (http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/1678/apc-smart-ups-1500-the-p...) this  seems to be normal position for the type of overload protector.

We have followed the troubleshoot in the manual, changed the fuse in the plug and tested the utility power supply by connecting a handheld power tool which worked fine.

Any help at all will be appreciated!

Thanks,

Bernard.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

You're very welcome. Let me know if you have any other questions I could help with regarding this.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

Do you still have the old battery to try and connect to see if the  UPS turns on?  Was the UPS on  with the old battery immediately before you replaced it or did it sit a while before you were able to get the replacement?

Usually these units will turn on with no battery connected. Only if they have been sitting for a while where the capacitors are  completely discharged will they often require a "jumpstart."

What happens if you remove the AC power/unplug the UPS from the wall and then hold down the  test button  - does it beep or do anything? Does the new RBC7 measure any DC voltage (if you happen to have a voltmeter available)?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

Hi Angela,

Thank you for your response!

We still have the old battery.  With the old battery in the UPS, the UPS wil l not turn on.  We turned off the machine  (connected to the UPS) and  the UPS  about  10 days ago while we waited on the replacement battery.

As you suggested, I've unplugged the UPS from the wall and held down the test button - unfortunately, the UPS didn't beep, the lights didn't flash or anything like  that. I don't have a voltmeter  available this evening but I'll check this tomorrow and I'll let you know.

Thank you for your help Angela!

Bernard.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

You're welcome! I'll see if I can come up with any other ideas too. Coldstarting the UPS (trying to  turn the UPS when it is unplugged by holding down the test) at least eliminates any input power problems.  Though, this was a genuine battery from APC, right? Does it have a serial number on it - to validate the age?  Or was this an RBC from a third party?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

That's good that it isn't an input power problem. Yes, the replacement battery is a genuine RBC7 which we purchased from APC.  The old battery (which required replacing)  is also a genuine RBC7.  The  old and new batteries both have serial numbers on them.  

Thanks again for your help, Angela. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

Hi Angela,

I checked the voltage of  new battery (25.8 V) and the old battery (10.2 V) earlier this morning. 

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

Hmm, OK.  So yes, that new battery is good voltage.  Though, I'd have to say the UPS appears to be the culprit if unplugging it from AC power with the new battery securely connected  while holding the "test" button does not give you any beeps or activity. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

Ah no, I was hoping that the UPS  wasn't the issue and that there was something  we could do  to fix it. In your opinion, do you think we should just replace it or would it be worth getting it serviced?  

Thanks for all your help, Angela!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

I think it  might be worth while to look into something like the Trade-UPS program (to trade in this UPS for credit towards a new one) so that you could evaluate the cost of a new unit with new warranty versus a repair. I am not sure what it could be  but I do think I would at least see if you do have any local repair options available while weighing a Trade UPS too.

Here is a link - it seems like its not available in all countries but if it is in yours once you check the website, you could get a ball park of understanding what the trade in value is of the UPS. We also provide return shipping of the unit you're trading in (at least in the US)-> http://buy.apc.com/commerce/storefronts/tradeups/tradein.aspx?storefrontcode=apcetu&countrycode=us&l... 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

Great, we weren't aware of the Trade-UPS program - I notice the UK is on it. Thank you for all your help, Angela!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

0 Likes
0
6109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:31 PM . Last Modified: ‎2024-03-19 12:06 AM

You're very welcome. Let me know if you have any other questions I could help with regarding this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore