APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:19 AM . Last Modified: 2024-03-18 12:33 AM
Hello, I have Smart-UPS X 1500 with AP9630. Everything is fine and working. But during power outage the network card cant read data from UPS.
It says "UPS: Lost the local network management interface-to-UPS communication." I have no data from UPS during power outage, so I cant see remaining backup time in my Cacti graphs and so on.
Could you give me an advice please?
Here is my configuration...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:19 AM . Last Modified: 2024-03-18 12:32 AM
OK, thank you both!
I will try cold reset and braindead my UPS.
I have reset NMC management interface already.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:19 AM . Last Modified: 2024-03-18 12:33 AM
Hi Jakub,
This is typically an issue with the logic of the UPS itself. What you could try yourself is a Brain Dead procedure, this is essentially the same as restarting your computer, you can follow the instructions outlined in the FAQ below.
http://www.apc.com/us/en/faqs/index?page=content&id=FA156611
If you are still experiencing issues after that, I would recommend you call into our tech support line for further support.
- Ben
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:19 AM . Last Modified: 2024-03-18 12:33 AM
You could also try to restart the AP9630's management interface first too which is a little less intrusive than restarting the UPS. To do this, go to Control->Network->Reset/Reboot and choose the first option, Reboot Management Interface. This has no affect on the UPS output. It is a quick step to try before what Ben suggested which very well could also be needed later.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:19 AM . Last Modified: 2024-03-18 12:32 AM
OK, thank you both!
I will try cold reset and braindead my UPS.
I have reset NMC management interface already.
Link copied. Please paste this link to share this article on your social media post.