SMC1500i Go To Battery Mode

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMC1500i Go To Battery Mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
8
1483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:32 AM

SMC1500i Go To Battery Mode

Since I have it first about a week a go, when I plugged the UPS to power socket and then turn it on, the ups will on by using electricity power and then go to battery mode for a couple second and then back to electricity power (I always unplugged the UPS from power wall if I'm not using it). But now, it doesn't go to to the battery anymore when I plugged the UPS to power socket and then turn it on. Is there a problem with my UPS?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

Ohhh, so it's something that can be configured right? So can you inform me how to enable it? Maybe I change something on the UPS or software that I'm not aware change the self test on the start up.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:32 AM

The UPS is only supposed to go to battery if there is a power failure.  If your power is on and it's not on the battery then it's fine.

The UPS will normally perform a self test when you first switch it on.  I am not sure why it would stop doing this but you can usually press the power on button when the UPS is already on to perform an extra self test.

If there is a problem with the UPS, the software you are using to communicate with the UPS will tell you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:32 AM

Ahhh, so it called self-test. Is this self-test when the UPS turn on can be disable or enable? If it can be disable or enable, maybe I accidentally turn if off (maybe). So how can I enable it again?

Or, if it can't be disable, is my UPS broken?

Reply

Link copied. Please paste this link to share this article on your social media post.

Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:32 AM

I'm not sure - try the self test manually and see if it works!  If so then there's nothing wrong.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

I just try the self test manually, and it works.

But I'm still curious about this self test when the UPS turn on. What happened with my UPS actually. Is there any APC technical support that can help me answer this?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

Hi,

The UPS performs an internal self-test every 14 days, and at start up unless configured by the user not to. The internal self-test checks the integrity of the battery. If the battery fails the self-test, the LCD screen will display the failure. This is a WARNING that the battery may be near the end of its life, replacement is typically recommended within 2-4 weeks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
0
1486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

Ohhh, so it's something that can be configured right? So can you inform me how to enable it? Maybe I change something on the UPS or software that I'm not aware change the self test on the start up.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

Hi,

You can configure when a self-test runs using PowerChute Business Edition Agent. 

YzB%2Bq%2FWJfppkFvlqfY5GtA%3D%3D.pngYzB%2Bq%2FWJfppkFvlqfY5GtA%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:20 AM . Last Modified: ‎2024-03-18 12:32 AM

Thanks a lot, the self-test back again when the UPS turn on now

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore