Smart-UPS SRT 8000 - Alarm Bypass Not In Range : High Voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SRT 8000 - Alarm Bypass Not In Range : High Voltage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
4
2194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

Smart-UPS SRT 8000 - Alarm Bypass Not In Range : High Voltage

We just installed this unit next to a SRT 10000 we have.  I am getting the critical Alarm Bypass not in range ; high voltage

When I powered it up on the UPS console screen I had a choice of 208 or 240vac input voltage.  I chose 208.

It appears that the actual input voltage is 240 according to the UPS Status screen in the Management Card.

This UPS is feeding 2 step down transformers to 120vac.  No load is on the UPS at this time.

The last time the alarm shows in the log it occurred 6 days ago.  Is there a special way to clear the alarms?

Thank you,

Jim R 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 8000
  • smart-ups
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
2193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

Hi Jim,

Since you have 240 input voltage the reason you were getting bypass not in range was because you had 240 in and 208 out. The unit was warning you that if it needed to go to bypass it would not because it did not want to provide a voltage of 240 when you were outputting 208 to your load. After changing the output to 240 volts that alarm should clear as the input matches the output (sounds like it did clear). 

One thing to be aware of though is that since we are outputting 240 volts now the output of your transformer will not be 120 volts as expected. The transformer is not an isolation transformer and is a fixed ratio designed to work with 208volts input. Since it now has 240 volts input, the actual output of the transformer will be about 138 volts. Please make sure your equipment would be able to handle this before connecting it. The math is below.

208volts in/120volts out = 1.733333 
240 volts in/1.733333=238volts out

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
2193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

Jim,

It is useful to know why you are using the transformers. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
2193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

Here is the fix for my situation-

In the Network Management app go to Control> Outlet Group Control.

Select all of the groups and select the action Off Immediately

Go to Configuration? Power Settings

Change the Rated Output voltage to 240 VAC  (make sure that in the status for the UPS the actual input is also 240)

Select Apply

Turn on all of the Outlet Groups

Alarm is cleared.

Jim R

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
2194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

 

Chris,

The output of the UPS is 208/240 and the step down transformers connected to it provides the 110vac needed for my servers etc...

APC Step-Down Transformer 2U Rackmount 208V Input, 120V 24A Output, (12) 5-20R Outlets APC Part Number APC9626

Jim R

 

 

 

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
2194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

Hi Jim,

Since you have 240 input voltage the reason you were getting bypass not in range was because you had 240 in and 208 out. The unit was warning you that if it needed to go to bypass it would not because it did not want to provide a voltage of 240 when you were outputting 208 to your load. After changing the output to 240 volts that alarm should clear as the input matches the output (sounds like it did clear). 

One thing to be aware of though is that since we are outputting 240 volts now the output of your transformer will not be 120 volts as expected. The transformer is not an isolation transformer and is a fixed ratio designed to work with 208volts input. Since it now has 240 volts input, the actual output of the transformer will be about 138 volts. Please make sure your equipment would be able to handle this before connecting it. The math is below.

208volts in/120volts out = 1.733333 
240 volts in/1.733333=238volts out

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of