Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Smart-UPS SRT 8000 - Alarm Bypass Not In Range : High Voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SRT 8000 - Alarm Bypass Not In Range : High Voltage
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
rhodesj2314_apc
Crewman rhodesj2314_apc
Crewman

Posted: ‎2021-06-30 10:55 PM

0 Likes
4
619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 10:55 PM

Smart-UPS SRT 8000 - Alarm Bypass Not In Range : High Voltage

This was originally posted on APC forums on 12/30/2015


We just installed this unit next to a SRT 10000 we have.  I am getting the critical Alarm Bypass not in range ; high voltage

When I powered it up on the UPS console screen I had a choice of 208 or 240vac input voltage.  I chose 208.

It appears that the actual input voltage is 240 according to the UPS Status screen in the Management Card.

This UPS is feeding 2 step down transformers to 120vac.  No load is on the UPS at this time.

The last time the alarm shows in the log it occurred 6 days ago.  Is there a special way to clear the alarms?

Thank you,

Jim R 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 8000
  • smart-ups
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:55 PM

0 Likes
0
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 10:55 PM

This was originally posted on APC forums on 12/30/2015


Hi Jim,

Since you have 240 input voltage the reason you were getting bypass not in range was because you had 240 in and 208 out. The unit was warning you that if it needed to go to bypass it would not because it did not want to provide a voltage of 240 when you were outputting 208 to your load. After changing the output to 240 volts that alarm should clear as the input matches the output (sounds like it did clear). 

One thing to be aware of though is that since we are outputting 240 volts now the output of your transformer will not be 120 volts as expected. The transformer is not an isolation transformer and is a fixed ratio designed to work with 208volts input. Since it now has 240 volts input, the actual output of the transformer will be about 138 volts. Please make sure your equipment would be able to handle this before connecting it. The math is below.

208volts in/120volts out = 1.733333 
240 volts in/1.733333=238volts out

See Answer In Context

Reply
Share
Replies 4
NWIGenerator_apc
Crewman NWIGenerator_apc
Crewman

Posted: ‎2021-06-30 10:55 PM

0 Likes
0
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 10:55 PM

This was originally posted on APC forums on 12/30/2015


Jim,

It is useful to know why you are using the transformers. 

Reply
Share
rhodesj2314_apc
Crewman rhodesj2314_apc
Crewman

Posted: ‎2021-06-30 10:55 PM

0 Likes
0
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 10:55 PM

This was originally posted on APC forums on 12/30/2015


Here is the fix for my situation-

In the Network Management app go to Control> Outlet Group Control.

Select all of the groups and select the action Off Immediately

Go to Configuration? Power Settings

Change the Rated Output voltage to 240 VAC  (make sure that in the status for the UPS the actual input is also 240)

Select Apply

Turn on all of the Outlet Groups

Alarm is cleared.

Jim R

Reply
Share
rhodesj2314_apc
Crewman rhodesj2314_apc
Crewman

Posted: ‎2021-06-30 10:55 PM

0 Likes
0
619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 10:55 PM

This was originally posted on APC forums on 12/30/2015


 

Chris,

The output of the UPS is 208/240 and the step down transformers connected to it provides the 110vac needed for my servers etc...

APC Step-Down Transformer 2U Rackmount 208V Input, 120V 24A Output, (12) 5-20R Outlets APC Part Number APC9626

Jim R

 

 

 

 

Reply
Share
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:55 PM

0 Likes
0
619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 10:55 PM

This was originally posted on APC forums on 12/30/2015


Hi Jim,

Since you have 240 input voltage the reason you were getting bypass not in range was because you had 240 in and 208 out. The unit was warning you that if it needed to go to bypass it would not because it did not want to provide a voltage of 240 when you were outputting 208 to your load. After changing the output to 240 volts that alarm should clear as the input matches the output (sounds like it did clear). 

One thing to be aware of though is that since we are outputting 240 volts now the output of your transformer will not be 120 volts as expected. The transformer is not an isolation transformer and is a fixed ratio designed to work with 208volts input. Since it now has 240 volts input, the actual output of the transformer will be about 138 volts. Please make sure your equipment would be able to handle this before connecting it. The math is below.

208volts in/120volts out = 1.733333 
240 volts in/1.733333=238volts out

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc