Old 3000XL fault
  • Old 3000XL fault
Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:34 AM
1278
Old 3000XL fault
I've an old Smart-UPS 3000XL, perfectly working.
I've turned off the unit for a while (because I moved on another room), then turned on.
Now, this is the error.
https://www.youtube.com/watch?v=N7jtXSHgntw
Welded relais?
Which one?
How I can get a service manual with schematic?
Thanks.
Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM
Many thanks for your answer, Michael.
Batteries are ok, I'm sure.
I'll try to disassemble and test any serviceable part (relais, condenser, diode, etc).
Thanks again.
Tano.
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander
HI Tano,
The combination of these lights shows a fault of "output overvoltage." I wouldn't think it is a relay issue but there is no way to be sure. Unfortunately, we do not provide schematics for our units.
You can try a brain dead procedure by unplugging it from the wall and disconnecting the battery for 30 seconds. Since the unit was sitting for a while the batteries might have discharged so if you have a unit that uses the same batteries you can try swapping them out. I would be hesitant to recommend buying new batteries as I would not want you to put money into a dead unit.
If you continue to see the same behavior after the bran dead I think you best option would be to utilize our trade-ups program where you get a 15-20%  on a new unit and we pay for the shipping back of your old one to recycle.
Thanks again.
Tano.