Smart-UPS RT 3000 XL with rapid change and low voltage?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 3000 XL with rapid change and low voltage?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:57 PM . Last Modified: ‎2024-03-01 12:13 AM

0 Likes
1
3650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:57 PM . Last Modified: ‎2024-03-01 12:13 AM

Smart-UPS RT 3000 XL with rapid change and low voltage?

I am not sure why this is happening???

Data Center in a shop environment.  Every couple of weeks I get a ton of emails from one of my 3000's that it has switched to battery power for this: "On battery power in response to rapid change of input." or this: "Bypass not in range ; low voltage." I have two 3000's but the other doesnt seem to have any issues. Not sure if it makes a difference, but the one with no issues breakers are in a different electrical panel.  I have attached the logs and data.  I would certainly appreciate if anyone can shed some light.

Thanks!

other info:

Last Battery Transfer: Unacceptable utility voltage rate of change
Battery Temperature: 27.8°C
Runtime Remaining: 1hour 12min 12sec
UPS Input    
Input Voltage: 215.5 VAC @ 60.0 Hz
 
UPS Output  
Output Voltage: 208.0 VAC @ 60.0 Hz
Load Current: 8.5 Amps
 
Output VA: 59.2 %
Output Watts: 83.4 %
Battery Status  
State of Charge: 100.0 %
Battery Voltage: 218.3 VDC
Num of External Batteries: 1 

Model: Smart-UPS RT 3000 XL
SKU: SURTD3000XLT
Serial Number: QS1402270771
Firmware Revision: 5.1 (ID5)
Manufacture Date: 01/08/2014
 
Apparent Power Rating: 3000 VA
Real Power Rating: 2100 W

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • problem
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:57 PM . Last Modified: ‎2024-03-01 12:13 AM

0 Likes
0
3650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:57 PM . Last Modified: ‎2024-03-01 12:13 AM

Hi,

The rapid change in voltage is listed a little bit here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156546 

Depending on how fast it is actually happening, the data log may not be able to catch it so it may not be obvious. I do see a few brief periods where your input voltage is dipping a little lower than it usually is in the Vmin column in the data log.

Bypass not in range messages are generated whenever the AC input voltage goes outside of the acceptable bypass criteria. Some of these settings are available to check in the Configuration->Power Settings in the management interface. This means that if your UPS needs to go to bypass while that alarm is active, it won't be able to. A UPS of this type will go to bypass because of like a fault or overload type condition. Normally, if a fault or overload occurs, the UPS will try to go to bypass (AKA run off of utility power) as to keep your load up rather than turning off completely.

I hope that helps clarify. Regardless, if it is frequent and happening regularly, it is an issue with utility power or something at that panel. A dip in voltage could indicate a high current draw on that panel/phase/circuit if it is not happening on the other panel. It may require an electrician to review but the UPS is just alarming to you that there is a problem and there is not much that can be done by the UPS besides alarm you. I don't see anything here that would point to the UPS causing the issue as the alarms refer to something going on with input utility power to the UPS.

I am not saying to go definitely spend money and do this but for situations like this, it may be helpful to leave a meter or oscilliscope running off of this panel or input feed to the UPS in order to see if it shows any abnormalities in the waveform showing the voltage drops. The UPS doesn't have the ability to capture waveforms or anything itself unfortunately.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:57 PM . Last Modified: ‎2024-03-01 12:13 AM

0 Likes
0
3651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:57 PM . Last Modified: ‎2024-03-01 12:13 AM

Hi,

The rapid change in voltage is listed a little bit here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156546 

Depending on how fast it is actually happening, the data log may not be able to catch it so it may not be obvious. I do see a few brief periods where your input voltage is dipping a little lower than it usually is in the Vmin column in the data log.

Bypass not in range messages are generated whenever the AC input voltage goes outside of the acceptable bypass criteria. Some of these settings are available to check in the Configuration->Power Settings in the management interface. This means that if your UPS needs to go to bypass while that alarm is active, it won't be able to. A UPS of this type will go to bypass because of like a fault or overload type condition. Normally, if a fault or overload occurs, the UPS will try to go to bypass (AKA run off of utility power) as to keep your load up rather than turning off completely.

I hope that helps clarify. Regardless, if it is frequent and happening regularly, it is an issue with utility power or something at that panel. A dip in voltage could indicate a high current draw on that panel/phase/circuit if it is not happening on the other panel. It may require an electrician to review but the UPS is just alarming to you that there is a problem and there is not much that can be done by the UPS besides alarm you. I don't see anything here that would point to the UPS causing the issue as the alarms refer to something going on with input utility power to the UPS.

I am not saying to go definitely spend money and do this but for situations like this, it may be helpful to leave a meter or oscilliscope running off of this panel or input feed to the UPS in order to see if it shows any abnormalities in the waveform showing the voltage drops. The UPS doesn't have the ability to capture waveforms or anything itself unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore