I am not sure why this is happening???
Data Center in a shop environment. Every couple of weeks I get a ton of emails from one of my 3000's that it has switched to battery power for this: "On battery power in response to rapid change of input." or this: "Bypass not in range ; low voltage." I have two 3000's but the other doesnt seem to have any issues. Not sure if it makes a difference, but the one with no issues breakers are in a different electrical panel. I have attached the logs and data. I would certainly appreciate if anyone can shed some light.
Thanks!
other info:
Last Battery Transfer: | Unacceptable utility voltage rate of change | ||
Battery Temperature: | 27.8°C | ||
Runtime Remaining: | 1hour 12min 12sec | ||
UPS Input | |||
Input Voltage: | 215.5 VAC | @ 60.0 Hz | |
UPS Output | |||
Output Voltage: | 208.0 VAC | @ 60.0 Hz | |
Load Current: | 8.5 Amps | ||
Output VA: | 59.2 % | ||
Output Watts: | 83.4 % | ||
Battery Status | |||
State of Charge: | 100.0 % | ||
Battery Voltage: | 218.3 VDC | ||
Num of External Batteries: | 1 |
Model: | Smart-UPS RT 3000 XL |
SKU: | SURTD3000XLT |
Serial Number: | QS1402270771 |
Firmware Revision: | 5.1 (ID5) |
Manufacture Date: | 01/08/2014 |
Apparent Power Rating: | 3000 VA |
Real Power Rating: | 2100 W |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:57 PM
This reply was originally posted by Angela on APC forums on 6/30/2015
Hi,
The rapid change in voltage is listed a little bit here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156546
Depending on how fast it is actually happening, the data log may not be able to catch it so it may not be obvious. I do see a few brief periods where your input voltage is dipping a little lower than it usually is in the Vmin column in the data log.
Bypass not in range messages are generated whenever the AC input voltage goes outside of the acceptable bypass criteria. Some of these settings are available to check in the Configuration->Power Settings in the management interface. This means that if your UPS needs to go to bypass while that alarm is active, it won't be able to. A UPS of this type will go to bypass because of like a fault or overload type condition. Normally, if a fault or overload occurs, the UPS will try to go to bypass (AKA run off of utility power) as to keep your load up rather than turning off completely.
I hope that helps clarify. Regardless, if it is frequent and happening regularly, it is an issue with utility power or something at that panel. A dip in voltage could indicate a high current draw on that panel/phase/circuit if it is not happening on the other panel. It may require an electrician to review but the UPS is just alarming to you that there is a problem and there is not much that can be done by the UPS besides alarm you. I don't see anything here that would point to the UPS causing the issue as the alarms refer to something going on with input utility power to the UPS.
I am not saying to go definitely spend money and do this but for situations like this, it may be helpful to leave a meter or oscilliscope running off of this panel or input feed to the UPS in order to see if it shows any abnormalities in the waveform showing the voltage drops. The UPS doesn't have the ability to capture waveforms or anything itself unfortunately.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:57 PM
This reply was originally posted by Angela on APC forums on 6/30/2015
Hi,
The rapid change in voltage is listed a little bit here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156546
Depending on how fast it is actually happening, the data log may not be able to catch it so it may not be obvious. I do see a few brief periods where your input voltage is dipping a little lower than it usually is in the Vmin column in the data log.
Bypass not in range messages are generated whenever the AC input voltage goes outside of the acceptable bypass criteria. Some of these settings are available to check in the Configuration->Power Settings in the management interface. This means that if your UPS needs to go to bypass while that alarm is active, it won't be able to. A UPS of this type will go to bypass because of like a fault or overload type condition. Normally, if a fault or overload occurs, the UPS will try to go to bypass (AKA run off of utility power) as to keep your load up rather than turning off completely.
I hope that helps clarify. Regardless, if it is frequent and happening regularly, it is an issue with utility power or something at that panel. A dip in voltage could indicate a high current draw on that panel/phase/circuit if it is not happening on the other panel. It may require an electrician to review but the UPS is just alarming to you that there is a problem and there is not much that can be done by the UPS besides alarm you. I don't see anything here that would point to the UPS causing the issue as the alarms refer to something going on with input utility power to the UPS.
I am not saying to go definitely spend money and do this but for situations like this, it may be helpful to leave a meter or oscilliscope running off of this panel or input feed to the UPS in order to see if it shows any abnormalities in the waveform showing the voltage drops. The UPS doesn't have the ability to capture waveforms or anything itself unfortunately.