I have two Smart-UPS RT 10000 XL's with transfer switches. I am not a power or UPS expert. The issue I have is that whenever there is a surge the units just shut down instead of using the batteries. So of course all my equipment shuts down and I have to come in a manually reboot the APC UPS's.
One of my UPS's says
Last Battery Transfer: | Unacceptable utility voltage rate of change |
Currently all the equipment is running on one unit and the mgt site says:
Input Voltage: | 240.4 VAC |
Output Voltage: | 207.0 VAC |
Runtime Remaining: | 34 minutes |
Last Battery Transfer: | Detection of a line voltage notch or spike |
I put a multimeter on each individual cell of batteries and they all check out. So Im thinking there is a configuration issue here. Attached is the config, data, and event files for each ups.
The only thing that has really changed is load at which it must support when commercial power fails has been significantly decreased.
Any help would be greatly appreciated
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:22 PM . Last Modified: 2024-02-14 02:20 AM
Hi Taylor,
I am seeing an inverter fault pop up in the event log. This might be the root cause of your problem. When an inverter fault shows up, the UPS itself should have the red X light up. I would contact your local support for further troubleshooting. I would have the log files ready to send over and be in front of the unit at a time that you can do some troubleshooting with the unit.
http://www.apc.com/support/contact/
Regards,
Mike
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:22 PM . Last Modified: 2024-02-14 02:20 AM
Hi Taylor,
I am seeing an inverter fault pop up in the event log. This might be the root cause of your problem. When an inverter fault shows up, the UPS itself should have the red X light up. I would contact your local support for further troubleshooting. I would have the log files ready to send over and be in front of the unit at a time that you can do some troubleshooting with the unit.
http://www.apc.com/support/contact/
Regards,
Mike
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.