Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Smart-UPS 2200 Failure.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 2200 Failure.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
radiosavage_apc
Crewman radiosavage_apc
Crewman

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
6
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

Smart-UPS 2200 Failure.

So of all of a sudden today a bunch of my workstations rebooted and a tech walked in to find this.  I know it has faulted but I really have no other clues.  This unit is only a little older than a year. 

8pbLHcxnJdol71K0%2F1KCWw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg8pbLHcxnJdol71K0%2F1KCWw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-01-29 11:37 PM

Hi,

The UPS has automatically switched to Bypass mode. Bypass mode operation is the result of an internal UPS fault or an overload condition while operating on utility power. You need to contact local technical support for assistance. You will find contact information here http://www.apc.com/site/support/index.cfm/contact-information/

When you call in you should be with the unit.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

radiosavage_apc
Crewman radiosavage_apc
Crewman

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
0
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

Thanks for the insight.  I would also like to note that once the dust settled it appears that one of the computers attached to the UPS has a failed power supply.  Perhaps that short caused it.  I will look at the suggested contact information and see about resetting the fault or other troubleshooting steps.

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

nghiatran2805_apc
Ensign nghiatran2805_apc
Ensign

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
0
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

help me ! 

diagrams APC2200 ? I replaced by main APC ! but I look find 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

nghiatran2805_apc
Ensign nghiatran2805_apc
Ensign

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
0
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

ic18 ic19 ic21 dead

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-01-29 11:37 PM

Hi,

The UPS has automatically switched to Bypass mode. Bypass mode operation is the result of an internal UPS fault or an overload condition while operating on utility power. You need to contact local technical support for assistance. You will find contact information here http://www.apc.com/site/support/index.cfm/contact-information/

When you call in you should be with the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

radiosavage_apc
Crewman radiosavage_apc
Crewman

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

Thanks for the insight.  I would also like to note that once the dust settled it appears that one of the computers attached to the UPS has a failed power supply.  Perhaps that short caused it.  I will look at the suggested contact information and see about resetting the fault or other troubleshooting steps.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

nghiatran2805_apc
Ensign nghiatran2805_apc
Ensign

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
0
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

Help me!i check main APC . It is dead 12 MOFET 4710 and IC HIP 4082

Reply

Link copied. Please paste this link to share this article on your social media post.

nghiatran2805_apc
Ensign nghiatran2805_apc
Ensign

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

help me ! 

diagrams APC2200 ? I replaced by main APC ! but I look find 
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-01-29 11:37 PM

Tran,

That is the overload LED, check to make sure you are not drawing to much current from the ups.

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

nghiatran2805_apc
Ensign nghiatran2805_apc
Ensign

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:20 PM . Last Modified: ‎2024-02-14 02:20 AM

ic18 ic19 ic21 dead

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of