So of all of a sudden today a bunch of my workstations rebooted and a tech walked in to find this. I know it has faulted but I really have no other clues. This unit is only a little older than a year.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-01-29 11:37 PM
Hi,
The UPS has automatically switched to Bypass mode. Bypass mode operation is the result of an internal UPS fault or an overload condition while operating on utility power. You need to contact local technical support for assistance. You will find contact information here http://www.apc.com/site/support/index.cfm/contact-information/
When you call in you should be with the unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-02-14 02:20 AM
Thanks for the insight. I would also like to note that once the dust settled it appears that one of the computers attached to the UPS has a failed power supply. Perhaps that short caused it. I will look at the suggested contact information and see about resetting the fault or other troubleshooting steps.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-02-14 02:20 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-02-14 02:20 AM
ic18 ic19 ic21 dead
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-01-29 11:37 PM
Hi,
The UPS has automatically switched to Bypass mode. Bypass mode operation is the result of an internal UPS fault or an overload condition while operating on utility power. You need to contact local technical support for assistance. You will find contact information here http://www.apc.com/site/support/index.cfm/contact-information/
When you call in you should be with the unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-02-14 02:20 AM
Thanks for the insight. I would also like to note that once the dust settled it appears that one of the computers attached to the UPS has a failed power supply. Perhaps that short caused it. I will look at the suggested contact information and see about resetting the fault or other troubleshooting steps.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-02-14 02:20 AM
Help me!i check main APC . It is dead 12 MOFET 4710 and IC HIP 4082
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-02-14 02:20 AM
help me !
diagrams APC2200 ? I replaced by main APC ! but I look find
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-01-29 11:37 PM
Tran,
That is the overload LED, check to make sure you are not drawing to much current from the ups.
Tom
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:20 PM . Last Modified: 2024-02-14 02:20 AM
ic18 ic19 ic21 dead
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.