Smart-UPS VT 40 kVA and mechanical bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS VT 40 kVA and mechanical bypass
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
chaser_apc
Crewman chaser_apc
Crewman

Posted: ‎2021-07-29 11:19 PM . Last Modified: ‎2024-02-14 10:10 PM

0 Likes
2
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:19 PM . Last Modified: ‎2024-02-14 10:10 PM

Smart-UPS VT 40 kVA and mechanical bypass

Hello,

We have Smart-UPS VT 40 kVA w/4 Batt Mod Exp to 4, int Maint Bypass, Parallel Capable SUVTP40KH4B4S, PS0813240713, Firmware Revision: 912.0405.I.

There are two critical mistakes:

In bypass in response to an internal hardware fault.

A power module fault exists.

Can we try to reboot to get rid of them?

Bellow – our adventures…

01.12.2015

07:53:13

UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.

01.12.2015

07:53:12

UPS: Restored the local network management interface-to-UPS communication.

01.12.2015

07:52:47

System: Network service started. System IP is 10.4.142.230 from manually configured settings.

01.12.2015

07:52:47

System: Warmstart.

01.12.2015

07:51:49

UPS: The output power is now turned on.

01.12.2015

07:51:48

UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.

01.12.2015

07:48:50

UPS: An internal mechanical bypass no longer exists.

01.12.2015

07:48:30

UPS: The output power is turned off.

01.12.2015

07:48:29

UPS: The external Switch Gear Q003 has opened.

01.12.2015

07:47:38

System: NTP update failure.

01.12.2015

07:47:28

UPS: The output power is now turned on.

01.12.2015

07:47:28

UPS: An internal mechanical bypass exists.

01.12.2015

07:47:28

UPS: The external Switch Gear Q003 has closed.

01.12.2015

07:46:04

UPS: An internal mechanical bypass no longer exists.

01.12.2015

07:46:03

UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

01.12.2015

07:45:47

UPS: The external Switch Gear Q003 has opened.

01.12.2015

07:45:41

UPS: The output power is turned off.

01.12.2015

07:45:28

UPS: An internal mechanical bypass exists.

01.12.2015

07:45:28

UPS: The external Switch Gear Q003 has closed.

01.12.2015

07:40:42

UPS: An input voltage or frequency problem prevents switching to bypass mode.

 

02.12.2015

01:53:51

UPS: In bypass in response to an internal hardware fault.

02.12.2015

01:53:51

UPS: A power module fault exists.

02.12.2015

00:15:39

UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

02.12.2015

00:15:18

UPS: An input voltage or frequency problem prevents switching to bypass mode.

02.12.2015

00:15:17

UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

02.12.2015

00:14:57

UPS: An input voltage or frequency problem prevents switching to bypass mode.

02.12.2015

00:14:57

UPS: In bypass in response to an internal hardware fault.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • bypass
  • mechanical
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
chaser_apc
Crewman chaser_apc
Crewman

Posted: ‎2021-07-29 11:19 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
0
3077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:19 PM . Last Modified: ‎2024-02-14 02:20 AM

Bill, thanks a lot for your reply.

We have done restart of the device. And “raw status” now is OK. No mistakes at all!

M States = 07 04 04

00000000 00000000

00000000 02

Thank you!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:19 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
3077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:19 PM . Last Modified: ‎2024-01-29 11:37 PM

Hello Vladimir,

I suggest first contacting the technical support group for your region:
http://www.apc.com/site/support/index.cfm/contact-information/ (choose your county with the drop down menu, so it will give you the approriate tech support phone

Reply

Link copied. Please paste this link to share this article on your social media post.

chaser_apc
Crewman chaser_apc
Crewman

Posted: ‎2021-07-29 11:19 PM . Last Modified: ‎2024-02-14 02:20 AM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:19 PM . Last Modified: ‎2024-02-14 02:20 AM

Bill, thanks a lot for your reply.

We have done restart of the device. And “raw status” now is OK. No mistakes at all!

M States = 07 04 04

00000000 00000000

00000000 02

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore