Smart UPS RM 3000VA - Not shutting down

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS RM 3000VA - Not shutting down
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
5
1659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

Smart UPS RM 3000VA - Not shutting down

Hi,

We are currently fitting a few new RM 3000 UPS' with NIC's, we can get the servers to shut down perfectly well but when it comes to powering them back up it is just not happenning.

At the moment I am just trialling with one server and one UPS to try and get the shutdown / startup correct.

I have tried a number of different things but it is not working, here is an overview of my UPS settings:

Config / Shutdown

Start of Shutdown
Low Battery Duration: 5 minutes
Shutdown Delay: 90 seconds
Maximum Required Delay: 2 minutes
Basic Signaling Shutdown: Enable

Duration of Shutdown
Sleep Time: 0.0 hours [0 to 359.9]

End of Shutdown
Minimum Battery Capacity: 30 %
Return Delay: 00 seconds


PowerChute® Shutdown Parameters

Maximum Required Delay: 5 minutes
On-Battery Shutdown Behavior: Restart when power is restored


Powerchute Client Shutdown Parameters

Events: Runtime Exceeded >

Yes, I want to shut down the system. Shutdown the system only when the event lasts this long (seconds): Enabled

Turn off the UPS after the shutdown finishes (Not applicable to Parallel Silcon UPS and Smart-UPS VT): Enabled



As I said the server shuts down fine, but the UPS itself never seems to shut down, therefore never drops the power to the server completely so the server is unable to power back on using it's AC Restore After Power Loss, which is set to Power On.

I know the AC restore setting works on this server as if I physically pull the power from the server then plug it back in the server powers up straight away.

What I want is to keep the current timing for shutdown of the servers, get the UPS to shut down it's output power until external power is restored and the battery is charged to 30%, then restore output power which then kicks the server back to life.

Can someone point me in the right direction please, I really need to get this sorted.

Thanks in advance

Lucas

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
1659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

I actually waited a while, not sure how long exactly. Will be doing another test this morning so will give it as long as possible.

Why do you say the ups will wait 5 mins to turn off?

I would like it to turn off as soon as the server is shutdown, reguardless of if the power comes back on during the shutdown, or if the battery is still charged, otherwise the servers wont come back up after a breif power outage. I don't want to have to wait for the batteries to hit 0% charge for it to shutdown as that may not happen.

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
1659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

Hi,

We are currently fitting a few new RM 3000 UPS' with NIC's, we can get the servers to shut down perfectly well but when it comes to powering them back up it is just not happenning.

At the moment I am just trialling with one server and one UPS to try and get the shutdown / startup correct.

I have tried a number of different things but it is not working, here is an overview of my UPS settings:

Config / Shutdown

Start of Shutdown
Low Battery Duration: 5 minutes
Shutdown Delay: 90 seconds
Maximum Required Delay: 2 minutes
Basic Signaling Shutdown: Enable

Duration of Shutdown
Sleep Time: 0.0 hours [0 to 359.9]

End of Shutdown
Minimum Battery Capacity: 30 %
Return Delay: 00 seconds


PowerChute® Shutdown Parameters

Maximum Required Delay: 5 minutes
On-Battery Shutdown Behavior: Restart when power is restored


Powerchute Client Shutdown Parameters

Events: Runtime Exceeded >

Yes, I want to shut down the system. Shutdown the system only when the event lasts this long (seconds): Enabled

Turn off the UPS after the shutdown finishes (Not applicable to Parallel Silcon UPS and Smart-UPS VT): Enabled



As I said the server shuts down fine, but the UPS itself never seems to shut down, therefore never drops the power to the server completely so the server is unable to power back on using it's AC Restore After Power Loss, which is set to Power On.

I know the AC restore setting works on this server as if I physically pull the power from the server then plug it back in the server powers up straight away.

What I want is to keep the current timing for shutdown of the servers, get the UPS to shut down it's output power until external power is restored and the battery is charged to 30%, then restore output power which then kicks the server back to life.

Can someone point me in the right direction please, I really need to get this sorted.

Thanks in advance

Lucas

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
1659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

Hi,

So far to test I have killed the power to the UPS and allowed the battery to run down to the shutdown threshold for the server, the server powers off successfully but the UPS seems to stay active rather than going to sleep and because it doesn't seem to enter sleep mode the server doesn't power back on.

If the server has the power physically pulled from it then put back in the server powers up again so I know the settings for AC Power Loss are correct on the server.

I thought the following setting should have been providing the behaviour I am looking for but it is enabled / ticked and still no joy:

Turn off the UPS after the shutdown finishes (Not applicable to Parallel Silcon UPS and Smart-UPS VT): Enabled

Any thoughts?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
1659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

Right, everything with your servers are fine, it's just a matter of getting the UPS to turn off when you want it to. How long did you wait after the servers turned off before giving up on the UPS? According to your settings, it looks like it'll wait at least 5m before shutting itself off. Maybe give it a few more minutes and see what it does?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
1659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

Based on the maximum required delay. That's the maximum amount of time the UPS needs to wait for your servers to shutdown, and it's generally the same value for what you put in the low battery duration field. It doesn't know when all of your servers are finished shutting down, so it will wait this amount of time AFTER a graceful shutdown has been initiated, then power off.

What's the firmware on the NMC (Administration > General > About > application/aos versions) and PCNS version?

Now that I look back at your first post... You actually have 2 maximum required delay values listed: one says 2m and one says 5m. Though like I said before, it's supposed to be the same value as the low battery duration, which you listed as 5m... Which one's the right one? I would assume 5m is correct. Maybe screenshots would help?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
1660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

I actually waited a while, not sure how long exactly. Will be doing another test this morning so will give it as long as possible.

Why do you say the ups will wait 5 mins to turn off?

I would like it to turn off as soon as the server is shutdown, reguardless of if the power comes back on during the shutdown, or if the battery is still charged, otherwise the servers wont come back up after a breif power outage. I don't want to have to wait for the batteries to hit 0% charge for it to shutdown as that may not happen.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of