Smart UPS 5000 not powering on

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 5000 not powering on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
4
2527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

Smart UPS 5000 not powering on

Hi all, N00b here.

I have 2x SmartUPS 5000 approx 8 years old.

After a recent power down one of the units would not boot up.  Lights flash once, the unit clicks (sounds like an internal relay) and then nothing.  Press the off button once and it clicks again.

I purchased brand new batteries for the unit and installed them.  Same result, Lights flash once, click and nothing.  

Ive tried holding down the power button - it results in one short beep, still no lights on the display.

Any suggestions?

Thanks, Garry.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
0
2525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

For anyone checking this thread in the future (Hi future human!)  I replaced the UPS rather than try to troubleshoot an old one. 

When the UPS was replaced I actually did test to see if disconnecting the power and reconnecting would bring it back up - it didnt.  the unit had died. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
0
2525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

Hi Garry,

Do you have the exact model and serial number of the unit (often located on the back of the unit on a white sticker) for reference?

I would recommend a procedure called a braindead:

1)Unplug the unit from the wall

2)Unplug any load on the unit

3)Disconnect all batteries

4)Hold down the off button for about 20 seconds

5)Reconnect everything and attempt to turn it on

If that does not work and you have purchased the correct new batteries for the unit without any results, the unit may need to be replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
0
2525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

Hi Jordon, thanks for the response.

Model:  DL5000RMI5U

SN:  AS0202160303

The unit's power is hard wired.  I'll need to get a sparky in to disconnect it and give it a try before spending the $$$ to replace it.

Thanks for any assistance,

Garry.

Reply

Link copied. Please paste this link to share this article on your social media post.

roger_apc
Ensign roger_apc
Ensign

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
0
2525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

You don't need to "disconnect" the unit, just turn off the supply circuit.  There may even be a switch in the area arount the UPS.  Otherwise, just turn off the circuit breaker that supplies that unit.

Cheers,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
0
2526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

For anyone checking this thread in the future (Hi future human!)  I replaced the UPS rather than try to troubleshoot an old one. 

When the UPS was replaced I actually did test to see if disconnecting the power and reconnecting would bring it back up - it didnt.  the unit had died. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore