Blade Server Power Requirements vs APC Symetra whip/breaker availability?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Blade Server Power Requirements vs APC Symetra whip/breaker availability?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
3
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

Blade Server Power Requirements vs APC Symetra whip/breaker availability?

Given the IBM and HP blade chassis reqirements for two 60amp circuits, what is APC offering to meet these needs within the Symetra 40k and 80k product lines? The designer tool drop-down list of breaker/plug combinations lists 30 amp and 50 amp but no 60 amp breaker. Also, the IBM 60 amp three phase PDU for the Blade Center H uses IEC60309 3P+G. This is not offered as a whip end.

Currently, I am just telling my customer's to purchase the symetra and have an electrician mount the breakers and plug ends. Is this what I need to keep doing? Given the mainstreaming of blade technology and the confusion over power, I would think APC would be all over it but I am not getting that warm and fuzzy feeling!

Tim Hollingworth, Sr Network Engineer
APC Gold Design Certified
ePlus Technology Inc.
thollingworth@eplus.com

Message was edited by: thollingworth

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

Here are the power cable options for the current IBM BladeCenter H chassis:

BladeCenter H Double 30A NEMA L6-30P (208V) 4.3M 25R5783
BladeCenter H Dual 32A IEC 309 P+N+G/16A IEC 320-C20 (230V) 4.3M25R5784
BladeCenter H Triple 16A IEC 320-C20 (200-240V) 2.8M 25R5785
BladeCenter H Double 30A KSC 8305 (220V) 4.3M (Korea) 25R5811
BladeCenter H Dual 32A AS/NZS 3112/16A IEC320-C20 (ANZ) 25R5812

BladeCenter H can have up to four 2900W power supplies. Comes standard with two.

For full use of all 14 blade slots, all four power supplies must be installed. This requires two power connections to be made to the chassis. The above cables are for two supplies, so you need to double that for full use of BladeCenter H

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

Hello Tim,

Currently, there is not an option for these power requirements. What you are recommending now will work, and may be the best current solution. We do know about the issues with Blade power requirements and are working on updating the Build-Out tool.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

Given the IBM and HP blade chassis reqirements for two 60amp circuits, what is APC offering to meet these needs within the Symetra 40k and 80k product lines? The designer tool drop-down list of breaker/plug combinations lists 30 amp and 50 amp but no 60 amp breaker. Also, the IBM 60 amp three phase PDU for the Blade Center H uses IEC60309 3P+G. This is not offered as a whip end.

Currently, I am just telling my customer's to purchase the symetra and have an electrician mount the breakers and plug ends. Is this what I need to keep doing? Given the mainstreaming of blade technology and the confusion over power, I would think APC would be all over it but I am not getting that warm and fuzzy feeling!

Tim Hollingworth, Sr Network Engineer
APC Gold Design Certified
ePlus Technology Inc.
thollingworth@eplus.com

Message was edited by: thollingworth

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:32 AM . Last Modified: ‎2024-03-18 11:11 PM

Here are the power cable options for the current IBM BladeCenter H chassis:

BladeCenter H Double 30A NEMA L6-30P (208V) 4.3M 25R5783
BladeCenter H Dual 32A IEC 309 P+N+G/16A IEC 320-C20 (230V) 4.3M25R5784
BladeCenter H Triple 16A IEC 320-C20 (200-240V) 2.8M 25R5785
BladeCenter H Double 30A KSC 8305 (220V) 4.3M (Korea) 25R5811
BladeCenter H Dual 32A AS/NZS 3112/16A IEC320-C20 (ANZ) 25R5812

BladeCenter H can have up to four 2900W power supplies. Comes standard with two.

For full use of all 14 blade slots, all four power supplies must be installed. This requires two power connections to be made to the chassis. The above cables are for two supplies, so you need to double that for full use of BladeCenter H

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore