Greetings,
we have a smart ups 3000 RM. It seems it has a problem to execute the command to run a self test.
Message:The set request failed. Please try again.
A restart of the APC-services is useless.
Only after a reconnect of the usb-cable to the same usb-port, we are able to start the self-test, but 1-2 days later there is the same problem.
Any ideas, how to solve this permanently ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:37 AM . Last Modified: 2024-03-14 12:38 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:37 AM . Last Modified: 2024-03-14 12:38 AM
Greetings,
we have a smart ups 3000 RM. It seems it has a problem to execute the command to run a self test.
Message:The set request failed. Please try again.
A restart of the APC-services is useless.
Only after a reconnect of the usb-cable to the same usb-port, we are able to start the self-test, but 1-2 days later there is the same problem.
Any ideas, how to solve this permanently ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:37 AM . Last Modified: 2024-03-14 12:38 AM
what software are you using to do this? it sounds like you are using powerchute business edition? please let us know the version under Help->About if you see that option or give us a screenshot of what you're looking at.
it may be beneficial to eventually reboot the UPS which we can look into after you give us a few more details so I would not do that yet.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:37 AM . Last Modified: 2024-03-14 12:38 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:37 AM . Last Modified: 2024-03-14 12:38 AM
Greetings,
we have a smart ups 3000 RM. It seems it has a problem to execute the command to run a self test.
Message:The set request failed. Please try again.
A restart of the APC-services is useless.
Only after a reconnect of the usb-cable to the same usb-port, we are able to start the self-test, but 1-2 days later there is the same problem.
Any ideas, how to solve this permanently ?