Symmetra Power Array

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra Power Array
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
9
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

Symmetra Power Array

Have a customer that has a Symmetra Power Array. I went out and saw his XR cabinet with batteries was flashing E7 and the batteries were not recognized throught the display. I ordered an SYXRCC and went out and replaced it. It recognized the batteries after about a minute, and then went from batteries showing 100%( the 4 in the unit) to 57%( showing other 8 in XR cabinet, for a total of 12 batteries.) Now, after 24 hours, he says it is still showing 57%. Can you guys give me some guidance on this on what I should do. Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

Have a customer that has a Symmetra Power Array. I went out and saw his XR cabinet with batteries was flashing E7 and the batteries were not recognized throught the display. I ordered an SYXRCC and went out and replaced it. It recognized the batteries after about a minute, and then went from batteries showing 100%( the 4 in the unit) to 57%( showing other 8 in XR cabinet, for a total of 12 batteries.) Now, after 24 hours, he says it is still showing 57%. Can you guys give me some guidance on this on what I should do. Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

How about doing a self test, or should I have him just unscrew the enable switch on the SYXRCC? Or do you want him to totally pull the card out and re-seat it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

He needs to be in bypass when re-seating the SYCC in back of the unit, correct?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

We re-seated both cards, and it is still showing 57%. What should I do next, is there something wrong with the unit or the cards? The SYXRCC is brand new from APC, so should I look at the SYCC?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

Hi Erin,

It is possible that the new SYXRCC card may not be accurately evaluating the batteries in its frame. Please have the customer call into our free phone support to see about getting a replacement card. It's very unlikely any other component is contributing to this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

That would be a very good troubleshooting step. Please let us know what happened.

If the issue does not clear, please reply back with the "raw status data" off the PowerView in the Diags menu for that specific battery frame.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

are you talking about me getting the raw status of each battery, or can I get it just for the frame?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

Just for the frame. Those first generation XR frames powered by the SYXRCC can only provide raw status for the frame.

DIAGS - > BATTs -> Frame X of X (frame in question) - > Raw Status Data

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

will do. thanks for your help and I reply as soon as I can.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:37 AM . Last Modified: ‎2024-03-14 12:38 AM

Have a customer that has a Symmetra Power Array. I went out and saw his XR cabinet with batteries was flashing E7 and the batteries were not recognized throught the display. I ordered an SYXRCC and went out and replaced it. It recognized the batteries after about a minute, and then went from batteries showing 100%( the 4 in the unit) to 57%( showing other 8 in XR cabinet, for a total of 12 batteries.) Now, after 24 hours, he says it is still showing 57%. Can you guys give me some guidance on this on what I should do. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore