Smart UPS 1500 won't turn on

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 1500 won't turn on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
13
5542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:02 AM

Smart UPS 1500 won't turn on

I just replaced the battery in my Smart UPS 1500 (SUA1500) that had gone bad, but now the unit won't turn on.  When I push the On/Test button it chirps once, but that is it.  It will cold start however, and if I hold down the On/Test button while running on battery (to display the utility voltage diagnostic) it indicates the utility voltage is in normal range (i.e. 3 leds lit).  Any idea what might be wrong?  I hope it is fixable, as it was a fairly expensive unit, and I'd hate to have to replace it.

Thanks for any help!  smile 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

RBC6 and RBC7 have a different physical size and a different connector from my findings so they are not interchangeable. I found something else interesting that I will message you on as well.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:02 AM

can you try pressing the sensitivity LED on the back of the unit while it is connected to AC power to lower it and toggle between high/medium/low?

Do you have a network management card or powerchute running so we can see what it reports (since input voltage is OK according to what you saw)?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:02 AM

Hi Angela,

Thanks for the help. I forgot to mention that I had tried changing the

sensitivity setting, but that had no effect either.

I've been using the UPS without any software, so I tried installing

Powerchute this morning to see if I could get more information.

Unfortunately, I ran into a snag with that. When installing the agent,

it hung on "checking for the presence of a UPS". Not sure why though,

as Windows XP clearly found it, with a battery symbol in icon tray as

well as an entry in Device Manager under Batteries. It was even giving

me an estimated "power remaining" readout. So it's a mystery why the

Powerchute installer couldn't find it. Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

My first thought is did you let it "auto detect" - if so, did you try specifying the communications port? Beyond that, nothing specific comes to mind immediately seeing as you mentioned XP saw it OK. The only other logical thing I thought of that maybe you did too is rebooting the computer as well as resetting the UPS and retrying (turn off UPS, remove from AC power, hold down off button (o) and wait for UPS to click and flash, then you can coldstart it again when ready to have it detected by the computer since it won't run off AC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

I tried the things you suggested, but to no avail. So I decided to try

installing Powerchute on a different PC (also Windows XP) and that

worked! So apparently there was something quirky with that particular

computer I had the UPS connected to.

With Powerchute installed, I was finally able to look at the

diagnostics. It showed a "Powered Failed" warning (no surprise) but

that was it. Everything else looked fine. The battery was operating at

normal conditions. The voltage was comfortably between the high and low

transfer limits. I didn't see anything that hinted at what the problem

might be. There is definitely power to unit, as its been charging the

battery also (as it should). Any other ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

can you post what you can see in the data log? (either screenshot or copy and paste with the column headings).

The other thing was did you see a "last transfer reason" anywhere?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

Angela,

Here's the screen shot data log. Where do I find "last transfer

reason"? Since I currently have to cold start the UPS to start it up,

would there be one? Thanks again for the help! -Pat

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

I am not seeing a screenshot or attachment embarassed

Also, depending what is going on, you have a good point - it may not show one or say "none recorded" but I figure its worth a look, especially when you're coldstarting when its connected to AC power and refusing it.

Assuming PCBE v9.X, check some place under Smart UPS 1500 menu. I only have a newer model and I am not seeing it listed but that is my educated guess on where it'd be.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

Uhm, for some reason the image I pasted didn't show.  Let's try again:

1265_2013-06-20_DataLog_from_Powerchute.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

Well, that output frequency is very strange for a coldstart. Should be 60.0 or 60.1. And I am not understand why there is no input frequency column..

Have you tried this on a different circuit or a different location? Maybe the input frequency is also not at 60 +/-3 and is out of range, causing the output to be off.

And I would definitely set sensitivity to low which would be if the LED on the back is off (or if you choose to do it via software).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

I have tried it on difference outlets, but not at a different site. It

worked fine for years though at this location, so I don't think it's the

site (or outlet). Not sure why the frequency is showing 62Hz, but since

it's running on battery only it must be something the UPS is doing.

So is it safe to assume the UPS is damaged and will need to be replaced? :^(

Pat

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

Does it show 62 when the AC power cable removed from the outlet too?

Before I spend more money, if it was me, I'd at least consider trying it on a different electrical circuit minimum in your location and ideally another site just to be sure. Very strange how this issue came about..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

Yes it does, and since I need it to work at this site, even if it

happened to work at another that would not help me. Anyway, I think I'm

ready to throw in the towel on this one. I feel pretty certain

something is wrong with the unit, and can't afford to spend any more

time on it. The question now is what to replace it with. An SMC1500

($330) or one of the competitor products at almost half the price?

Do you know if the SMC1500 uses the same battery as the SUA1500? If so,

that would be one argument for going with it (the battery in SUA1500 was

new). At least I could salvage that.

Thanks again for all your help. I appreciate it.

Pat

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

0 Likes
0
5538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:02 AM

RBC6 and RBC7 have a different physical size and a different connector from my findings so they are not interchangeable. I found something else interesting that I will message you on as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore