Hello,
I have a customer that has a SYAF16k Symmetra LX. Now, he wants to get this empty cabinet and add 5 batteries to this for extra runtime. His load is 47%, and has 19 minutes of runtime right now. If adding 5 batteries to the cabinet, what is he looking at as far as runtime? Any help is greatly appreciated. Thank you!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:06 AM . Last Modified: 2024-03-13 12:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:06 AM . Last Modified: 2024-03-13 12:01 AM
thank you so much, that's what I needed to know. You guys are great!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:06 AM . Last Modified: 2024-03-13 12:01 AM
Hi Erin,
Can you confirm how many power modules are installed in the 16k LX please? Then we can help give an accurate estimate. We will also assume this is with (4) batteries pre-installed in the LX..?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:06 AM . Last Modified: 2024-03-13 12:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:06 AM . Last Modified: 2024-03-13 12:01 AM
4 power modules, and yes, 4 batteries. Thank You!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:06 AM . Last Modified: 2024-03-13 12:01 AM
hi erin,
assuming all fresh batteries in both the LX and the five added in the XR frame, the best approximation I can give is 47 minutes.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:06 AM . Last Modified: 2024-03-13 12:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:06 AM . Last Modified: 2024-03-13 12:01 AM
thank you so much, that's what I needed to know. You guys are great!