error on Smart-UPS RT 6000 XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • error on Smart-UPS RT 6000 XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:01 AM

0 Likes
5
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-13 12:01 AM

error on Smart-UPS RT 6000 XL

Hi,

I have a problem with Smart-UPS RT 6000 XL. Management card shows these errors:


Smart-UPS RT 6000 XL : UPS_IDEN

3 Critical Alarms Present

In Bypass Due To Hardware Fault

Output Voltage Abnormal Due To Inverter Fault

Diagnostic Test Failure



Does anobody know what those errors mean and what I can do with that? battery defect?

I suppose the device is useless if a powercut happend?



The purchase date of the device is 2007


Thanks

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

0 Likes
0
1970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

Dear,

The warranty of the device is over.

In attach the event, data and config file.

Very thanks

See Answer In Context

Attachments
event.txt.zip
data.txt.zip
config.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:58 PM

0 Likes
0
1970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:58 PM

It seems like you have an inverter fault (hardware problem) and it is causing the other alarms. And yes, since its in bypass and no inverter is available, then it will just turn off during an outage.

This most likely will require a replacement or repair either under warranty or not.

If you want us to review further, you can also provide the event and data logs from the management card as outlined in the knowledge base -> http://www.apc.com/site/support/index.cfm/faq/ -> search for article ID FA156131

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

0 Likes
0
1970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

Hello,

Took a look. The event log seems to have cut off but I also see battery issues (presumably since its been stuck in bypass due to inverter fault) but I also see an instance where inverter fault cleared.

How old is the UPS/batteries? The NMC firmware is kind of old and assuming you've never upgraded it I am going to ball park the UPS itself is at least 5-6 years old.

There might be some hope for the UPS if we had known good fresh batteries to try and bring it online but I hate to tell you to buy fresh batteries and we are not able to recover it. Do you have any you could swap from a similar unit just for testing? The UPS cannot come online without good batteries and it might not even if the inverter fault is actually true (which i seem to think it is).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

0 Likes
0
1970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

Hello ,

The UPS/baterry is purchased in june 2007.

The firmware was never updated.

I have 2 battery connected to the UPS so maybe I can use one battery each time for the test for identify the bad battery?

Very thx

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

0 Likes
0
1970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

You mean external battery packs? Yes, we could try that but keep in mind that one battery module in the system could've damaged others. And if they are already from 2007, they are past their 3-5 year typical lifetime. But for the sake if ruling out the UPS, you could try it but I'd still be concerned if those external battery packs are also from that timeframe. The UPS must have around ~175vDC for its battery bus to be able to come online as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-12 11:57 PM

Dear,

The warranty of the device is over.

In attach the event, data and config file.

Very thanks

Attachments
event.txt.zip
data.txt.zip
config.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore