Smart UPS 1500 and serial cable connection

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 1500 and serial cable connection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
6
4850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

Smart UPS 1500 and serial cable connection

Hi, we have a Smart UPS 1500 (firmware revision 601.3.D) connected to a server running Windows 2003 Server. Originally it was hooked up with a USB connection. The software was installed (server, client, console) and ran fine, but now we want to run it off the serial cable instead. I disconnected the USB connection, connected the serial cable (original one supplied with UPS), and then I stopped and restarted the APC services. The computer now cannot communicate with the UPS. In the console it shows "UPS Communication Lost".

I went into the Console, then Device Properties, then asked it to show the Advanced items, then I expanded the Communications section, and finally highlighted UPS Communications. In the Port box it doesn't display anything other than "USB" as a connection type.

How do I get it working off serial?

Thanks for any help.

David

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
4845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

Hello,

To switch a UPS back to serial after using USB, you need to reset the internal memory by a process we call, "braindeading". To braindead a UPS, you need to power down the load, unplug the load, and power down the UPS. Then unplug the UPS from the wall power and turn it off. Once the UPS is off and unplugged, push and hold the Off button for about 10 seconds. You may hear a small click inside the UPS. The UPS is then considered "braindead".
Go ahead and power everything back up, and connect the serial cable. You will need to either reinstall the Agent portion of Business Edition, or change the comm settings through the Server and Console portion on this direct Agent.

Hope this helps. Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
4845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

Try unstalling, then reinstalling the software.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
4846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

Hello,

To switch a UPS back to serial after using USB, you need to reset the internal memory by a process we call, "braindeading". To braindead a UPS, you need to power down the load, unplug the load, and power down the UPS. Then unplug the UPS from the wall power and turn it off. Once the UPS is off and unplugged, push and hold the Off button for about 10 seconds. You may hear a small click inside the UPS. The UPS is then considered "braindead".
Go ahead and power everything back up, and connect the serial cable. You will need to either reinstall the Agent portion of Business Edition, or change the comm settings through the Server and Console portion on this direct Agent.

Hope this helps. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
4845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

Thanks, I'll have to wait for a window I can power down the server, but it sounds like it should do the trick.

Thanks again,

David

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
4845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

The brain-dead procedure is just a way to de-energize the unit. It has no affect on the network management card.

The only way to get back into the card is doing the reset procedure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
4845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

Greetings, just wondered how this worked for you?

I have a Smart UPS 1500 XLM that I fat fingered the ID and password on the administration acccount and not cannot access it.

I have read and understood the instructions to reset the defaults, but I wondered if brain deading the NW management card would wipe out the all the configuration so I do not have to hyperterminal into the UPS.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
4845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 PM . Last Modified: ‎2024-03-15 03:56 AM

Drats, I was afraid you were going to tell me that.

I have the instructions for this. Unfortunately, this is a remote site, so will have to perform the procedures after hours on my next planned visit.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore