Smart-UPS 1500 RM does not reposnd for one SNMP OID

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1500 RM does not reposnd for one SNMP OID
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
horizn_apc
Crewman horizn_apc
Crewman

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
12
3506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

Smart-UPS 1500 RM does not reposnd for one SNMP OID

Hi,

One of our newly installed Smart-UPS 1500 RM does not respond for "Current Output" OID in Nagios:

define service{
        use generic-service ;
        hostgroup_name 007-ups-all-apc
        service_description APC output current
        check_command check_snmp!-o .1.3.6.1.4.1.318.1.1.1.4.2.4.0 -C public -w 40 -c 50 -u A
        }

Error message from Nagios:

Current Status:
  UNKNOWN  
 (for 8d 0h 59m 45s)
Status Information: SNMP problem - No data received from host
CMD: /usr/bin/snmpget -t 1 -r 5 -m '' -v 1 [authpriv] 10.172.8.12:161 .1.3.6.1.4.1.318.1.1.1.4.2.4.0

Other APC UPSes (including RM 1500) are working properly. I've compared SNMP configuration on web interface to other UPS, and it seems to be configured in the same way. Management card has the same FW version like the rest of management cards.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:22 PM . Last Modified: ‎2024-03-01 12:00 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:22 PM . Last Modified: ‎2024-03-01 12:00 AM

These older style model UPSs that begin with SU, SUA, SUM, etc are unfortunately not firmware upgradable. In later 2009, they were replaced with models beginning with SMT/SMX which are firmware upgradable.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

Do you see this value within the web or telnet/ssh interfacefor this specific UPS?

Can you provide more detail on the exact model of the UPS i.e. SUA1500RM2U, SMT1500RM2U, etc

Reply

Link copied. Please paste this link to share this article on your social media post.

horizn_apc
Crewman horizn_apc
Crewman

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

Model is SUA1500RMI2U, and no I can't see values using web interface:

Load
Load Power: 50.0 %Watts

vs.

Load
Load Power: 53.9 %Watts
Apparent Load Power: 40.9 %VA
Load Current: 2.7 Amps

on the other SUA1500RMI2U UPS. Both management cards have the same software version: I found that both cards have different firmware installed.

1. (Broken)

Hardware Factory
   
Model Number: AP9630
Serial Number: ZA1422020734
Hardware Revision: 05
Manufacture Date: 05/30/2014
MAC Address: 00 C0 B7 86 9F 7E
Management Uptime: 0 Days 5 Hours 26 Minutes

Application Module
   
Name: sumx
Version: v6.1.1
Date: Mar 7 2014
Time: 12:05:01

APC OS (AOS)
   
Name: aos
Version: v6.1.1
Date: Mar 7 2014
Time: 11:52:49

APC Boot Monitor
   
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time:

13:35:57

2. Good:

Hardware Factory
   
Model Number: AP9630
Serial Number: ZA1422020248
Hardware Revision: 05
Manufacture Date: 05/30/2014
MAC Address: 00 C0 B7 86 A0 9D
Management Uptime: 12 Days 2 Hours 29 Minutes

Application Module
   
Name: sumx
Version: v6.2.0
Date: Aug 11 2014
Time: 16:23:22

APC OS (AOS)
   
Name: aos
Version: v6.2.0
Date: Aug 11 2014
Time: 16:14:01

APC Boot Monitor
   
Name: bootmon
Version: v1.0.8
Date: Apr 8 2014
Time: 10:59:40

So maybe it is possobile to upgrade firmware in UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

horizn_apc
Crewman horizn_apc
Crewman

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

installed this:

http://www.apc.com/tools/download/download.cfm?sw_sku=SFSUMX621&software_id=MFOI-9TPLH7&family=98&pa...

but still have no access to Current Load.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

So both are at v6.2.0 now or v6.2.1? Can you download the event.txt or go to the event log and export it for me to view? Either version and what you had before is OK for the AP9630 and what it should be. The UPSs themselves (SUA models) cannot be updated and would not be a factor here anyway.

Does this UPS by chance have anything else potentially connected to it - something to its serial or USB port? This UPS has a communication bus that is like a chain and if something in the chain is broken, then nothing may work. The serial port and SmartSlot that the AP9630 is installed in are on the same communication bus.

*Edit* saw your recent post. Is the NMC talking to the UPS now? The event log can tell me this. If you see UPS values in the web interface, then it means it is.

Reply

Link copied. Please paste this link to share this article on your social media post.

horizn_apc
Crewman horizn_apc
Crewman

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

On 8/4/2015 11:30 AM, Angela said:

So both are at v6.2.0 now or v6.2.1? Can you download the event.txt or go to the event log and export it for me to view? Either version and what you had before is OK for the AP9630 and what it should be. The UPSs themselves (SUA models) cannot be updated and would not be a factor here anyway.

Does this UPS by chance have anything else potentially connected to it - something to its serial or USB port? This UPS has a communication bus that is like a chain and if something in the chain is broken, then nothing may work. The serial port and SmartSlot that the AP9630 is installed in are on the same communication bus.

*Edit* saw your recent post. Is the NMC talking to the UPS now? The event log can tell me this. If you see UPS values in the web interface, then it means it is.

Yes, UPS is talking to NMC, however I am still in the same place. Nothing is connected to USB port, only three network switches to power sockets. Here is event log:

Network Management Card AOS v6.2.1
Smart-UPS & Matrix-UPS APP v6.2.1

Date        Time        Name    Contact    Location    System IP
08/04/2015    17:26:50    apc869F7E    Unknown    Unknown        10.172.8.12

Date        Time        User        Event    Code
08/04/2015    17:26:35    apc    Web user 'apc' logged in from 10.172.2.200.    0x0015
08/04/2015    16:43:46    System    CLI user 'apc' logged out from 10.172.2.200.    0x001E
08/04/2015    16:43:15    System    Web user 'apc' logged out from 10.172.2.200.    0x001F
08/04/2015    16:40:22    apc    CLI user 'apc' logged in from 10.172.2.200.    0x0014
08/04/2015    16:40:11    apc    Web user 'apc' logged in from 10.172.2.200.    0x0015
08/04/2015    16:40:01    Device    UPS: Restored the local network management interface-to-UPS communication.    0x0101
08/04/2015    16:39:59    System    Network service started. System IP is 10.172.8.12 from DHCP server 10.172.3.12 with 86390 second lease.    0x0007
08/04/2015    16:39:43    System    Network service started. IPv6 address FE80::2C0:B7FF:FE86:9F7E assigned by link-local autoconfiguration.    0x0007
08/04/2015    16:39:35    System    Network Interface restarted.    0x0002
08/04/2015    16:39:27    apc    Network Interface restarting. Web user request.    0x0009
08/04/2015    16:39:12    apc    Configuration change. Telnet server access.    0x0033
08/04/2015    16:33:42    apc    Web user 'apc' logged in from 10.172.2.200.    0x0015
08/04/2015    16:32:21    System    SSH/SCP: Host key generation complete.    0x0037
08/04/2015    16:32:20    System    Network service started. System IP is 10.172.8.12 from DHCP server 10.172.3.12 with 86390 second lease.    0x0007
08/04/2015    16:32:19    Device    UPS: Restored the local network management interface-to-UPS communication.    0x0101
08/04/2015    16:32:01    System    SSH/SCP: Host key generation started.    0x0037
08/04/2015    16:32:01    System    Network service started. IPv6 address FE80::2C0:B7FF:FE86:9F7E assigned by link-local autoconfiguration.    0x0007
08/04/2015    16:31:53    System    Network Interface restarted.    0x0002
08/04/2015    16:31:45    apc    Network Interface restarting. Web user request.    0x0009
08/04/2015    16:30:20    apc    Configuration change. SSH server access.    0x0033
08/04/2015    16:30:20    apc    Configuration change. Telnet server access.    0x0033
08/04/2015    16:27:11    apc    Web user 'apc' logged in from 10.172.2.200.    0x0015
08/04/2015    16:26:01    Device    UPS: Restored the local network management interface-to-UPS communication.    0x0101
08/04/2015    16:25:56    System    NTP update successful.    0x004A
08/04/2015    16:25:56    System    Configuration change.     0x0033
08/04/2015    16:25:54    System    Network service started. System IP is 10.172.8.12 from DHCP server 10.172.3.12 with 86390 second lease.    0x0007
08/04/2015    16:25:54    System    Configuration change. NTP enable.    0x0033
08/04/2015    16:25:45    System    Configuration change. User class.    0x0033
08/04/2015    16:25:42    System    Network service started. IPv6 address FE80::2C0:B7FF:FE86:9F7E assigned by link-local autoconfiguration.    0x0007
08/04/2015    16:25:39    System    Event Log cleared.    0x0013
08/04/2015    16:25:28    System    Network Interface restarted.    0x0002

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

Ok, so as of right now with this unit, do other OIDs work normally? I need to understand if this is an SNMP timeout, UPS not responding to only this OID, and if the web shows a valid value for this in the web interface right this second as your trying the OID/SNMP poll.

The event log to me shows right now that the UPS should be providing values. Is the data log populating normally right now?

Reply

Link copied. Please paste this link to share this article on your social media post.

horizn_apc
Crewman horizn_apc
Crewman

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

Hi Angela,

Yes, other OIDs works fine, UPS is not reponding only for that OID and Web interface does not show values for Load Current. Please see attached screen shots.

OEjaVO6z73YfJNI9bRoGCg%3D%3D.pngOEjaVO6z73YfJNI9bRoGCg%3D%3D.png

2pIElybak0lSPisTJhX41w%3D%3D.png2pIElybak0lSPisTJhX41w%3D%3D.png

JkGAJepMX4cVvvTQgNxgAQ%3D%3D.pngJkGAJepMX4cVvvTQgNxgAQ%3D%3D.png

Is it possible to reboot UPS, without cutting from power attached devices?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

Not all APC models support all of the OIDs in the APC MIB. Sometimes this is a limitation of the underlying UPS hardware and sometimes it is because the NMC application (APP) just thinks that a value isn't supplied by the UPS. Since the web interface does not show the load data either, this is not just a SNMP issue. Either the UPS isn't providing it or the NMC doesn't know how to ask for it from this particular model.

If you have multiple units of the exact same UPS model that are behaving differently, I would post the serial numbers (you can x out the last few characters if you want) and the firmware revision(s) of the UPS firmware, as well as the AOS and APP version numbers of the management card firmware.

If this is the only UPS you have of this exact model, I would update both the NMC firmware and the UPS firmware to the latest versions to see if that resolves the issue. NMC2 6.2.1 firmware for Smart-UPS is available here, but you'll have to wait and see what the APC people say about UPS firmware updates for your UPS model, based on the firmware revision in your existing unit.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

horizn_apc
Crewman horizn_apc
Crewman

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

OK, for problematic UPS:

Model: Smart-UPS 1500 RM
Serial Number: AS0846299480
Firmware Revision: 617.3.I
Manufacture Date:

11/13/08

Application Module
   
Name: sumx
Version: v6.2.1
Date: Feb 6 2015
Time: 14:10:13
APC OS (AOS)
   
Name: aos
Version: v6.2.1
Date: Feb 6 2015
Time: 14:00:57

APC Boot Monitor
   
Name: bootmon
Version: v1.0.8
Date: Apr 8 2014
Time: 10:59:40

same model, but working fine:

Model: Smart-UPS 1500 RM
Serial Number: AS0907231185
Firmware Revision: 667.18.I
Manufacture Date: 02/10/09

Application Module
   
Name: sumx
Version: v6.2.0
Date: Aug 11 2014
Time: 16:23:22

APC OS (AOS)
   
Name: aos
Version: v6.2.0
Date: Aug 11 2014
Time: 16:14:01

APC Boot Monitor
   
Name: bootmon
Version: v1.0.8
Date: Apr 8 2014
Time: 10:59:40

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

Have you verified both of their white stickers on the phyiscal units show the same exact variant - SUA1500RMI2U? I see they were manufactured at different times and have different firmware but they both report as the generic Smart-UPS 1500 RM. I agree with Terry that all UPS models don't support this value but if it is the same SKU, that is strange. Though, they could've made an internal change/upgraded the firmware without changing the SKU.

I do see that this is not supported by SURTA models, SU, and some SUA models.. but I don't have further specifics than that unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

horizn_apc
Crewman horizn_apc
Crewman

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:21 PM . Last Modified: ‎2024-03-01 12:01 AM

Yes, they both are Smart-UPS 1500 RM with the same SUA1500RMI2U on the white sticker. We have more UPSes of this model, and they all have the same SKU (SUA1500RMI2U) on the white sticker, however only two are fitted with NMC so far. Because I am planning to equip rest of them with NMC, so how can I upgrade UPS firmware then?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:22 PM . Last Modified: ‎2024-03-01 12:00 AM

0 Likes
0
3503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:22 PM . Last Modified: ‎2024-03-01 12:00 AM

These older style model UPSs that begin with SU, SUA, SUM, etc are unfortunately not firmware upgradable. In later 2009, they were replaced with models beginning with SMT/SMX which are firmware upgradable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of