SURT 8000VA RM 230V Minimum input current
  • SURT 8000VA RM 230V Minimum input current
Posted: ‎2021-07-07 11:22 PM . Last Modified: ‎2024-03-01 12:00 AM
905
Hi Folks,
Wondering if there's a minimum input current for the SURT 8000VA?
Thanks.
You're welcome. So the product page is here -> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT8000RMXLI
The answer appears to be a minimum input of 160V for the UPS to operate at a full load. I also double checked some technical specifications which said:
  • Input voltage range at full load 160 to 280VAC
  • Input voltage range at half load 100 to 280VAC
Can you clarify the model? SURT8000XLT or SURT8000XLI?
Usually there is no minimum current but rather a minimum input voltage to operate. Depending on the model, we can find that out for you.
Hi Angela,
Thanks for the quick response. It's an 8000RMXLI.