Hi Folks,
Wondering if there's a minimum input current for the SURT 8000VA?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 2024-03-01 12:00 AM
You're welcome. So the product page is here -> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT8000RMXLI
The answer appears to be a minimum input of 160V for the UPS to operate at a full load. I also double checked some technical specifications which said:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 2024-03-01 12:00 AM
Can you clarify the model? SURT8000XLT or SURT8000XLI?
Usually there is no minimum current but rather a minimum input voltage to operate. Depending on the model, we can find that out for you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 2024-03-01 12:00 AM
Hi Angela,
Thanks for the quick response. It's an 8000RMXLI.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 2024-03-01 12:00 AM
You're welcome. So the product page is here -> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT8000RMXLI
The answer appears to be a minimum input of 160V for the UPS to operate at a full load. I also double checked some technical specifications which said: