Smart-UPS 1000XL shuts down unexpectedly

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1000XL shuts down unexpectedly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

0 Likes
4
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

Smart-UPS 1000XL shuts down unexpectedly

I have a Smart-UPS 1000XL connected to a UXBP24 battery pack with four batteries. The UPS battery and all four batteries in the battery pack are brand new, fully charged with about a 31% load. Twice in the last three months this UPS has shut down unexpectedly. The first time, I was right next to it and it shut down completely with no beeps or lights flashing, as though I had manually shut it off. This of course immediately cut power to the entire rack that it powers. Any idea what the cause could be? Unfortunately, I did not have PowerChute running at the time (I do now). I know the UPS unit itself is 10 or 11 years old. Is it time to replace the UPS unit, and if so, is there an available one that would work with this same battery pack?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

0 Likes
0
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

The only thing I can think of is that 28 days is exactly twice the standard self-test interval of 14 days. It might be that there is something happening which causes the self-test to fail some of the time. It might be worthwhile to temporarily set the self-test to "never" and see if the problem stops happening. If that is the case, then there's something wrong which is causing a total failure ("lights out") during the self-test which will need to be investigated further. If the problem keeps happening, then this wasn't the cause of it. In either case, you definitely want to re-enable scheduled self-tests or the first time you'll know the UPS doesn't work is during the next power outage.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

This is tough to say without looking at log data to see what is reported. It could be either be batteries (is the external battery connector connected securely) or the UPS unit and based on what you said and described, it does not make me lean towards one more than the other unfortunately.

After making arrangements with a non critical load, you could trip the upstream breaker to simulate a power outage to the UPS as one test to see what happens when the UPS loses AC input. If that works, then that's one thing to rule out but it still wouldn't necessarily rule out the UPS as the culprit but is at least a start to verify a part of the UPS's operation.

We do have a Smart-UPS XL compatibility charge for battery packs here if you do end up going with a new or different UPS (only older models will likely work with this XL BP)-> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA156524 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

Thanks for your reply. This happened again a few days ago and I'm seeing a few interesting facts.  This issue has happened exactly 28 days apart, three times in a row (although at different times of the day). This last time it happened I found the "Battery Charge" lights on the right side of the panel were all lit - can't remember if other lights were lit or not, but it was not making any sound or providing any power.  That is, everything plugged into it was powered down.  I hit the power button and the unit powered off, then I hit the Test button and the unit and everything plugged into it powered up.  The log files don't show much.  I see a week or so before that it did a self-test and passed.  It doesn't show any lost communication until I powered it down and back up. I failed to mention earlier that we have occasionally experienced very brief power outages to the building, during which the unit has responded appropiately and switched to battery power. Does this make any sense?  Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

Hi Rick,

I am just as puzzled as you unfortunately. I am not sure what the every 28 days part means either. It does not align with anything I know of on the product side and I assume it did not mean anything to you regarding something in the environment, regular building maintenance schedule (beyond planned power outages), etc?

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:23 PM . Last Modified: ‎2024-02-29 11:59 PM

The only thing I can think of is that 28 days is exactly twice the standard self-test interval of 14 days. It might be that there is something happening which causes the self-test to fail some of the time. It might be worthwhile to temporarily set the self-test to "never" and see if the problem stops happening. If that is the case, then there's something wrong which is causing a total failure ("lights out") during the self-test which will need to be investigated further. If the problem keeps happening, then this wasn't the cause of it. In either case, you definitely want to re-enable scheduled self-tests or the first time you'll know the UPS doesn't work is during the next power outage.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore