SURT8000xli not power ON

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT8000xli not power ON
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
11
2569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

SURT8000xli not power ON

Hello my name is Vitaly and i from Russia

i buy this UPS 12.2012

SURT8000xli -QS1235350546

in 03.2013 UPS not power up, i call to my seller!

UPS garanty and ship 04.2013  to Moscow  repair, after 2-3 month  service send me email

and tell me my UPS lost warranty about this UPS have chip (noname) on motherboard 0P7641

please see image and tell me what it is)

What do you think? that circled in the photo? where this item?

We did not open it, we refuse to guarantee that we ourselves say there soldered capacitor

1282_7641.jpg

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 0p7641
  • 8000
  • surt
  • surt8000xli
  • xli
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
0
2569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

hello vitaly the component that you show in the picture is a Termistor. you can see in  the board appear the name of the component  TH701 means "Termistor 701", and this component is a part of the power supply and if this component is damaged the ups can´t turn on.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

Hi vitaliy

These UPSs are not user serviceable typically and if it failed under warranty, the entire unit should've been swapped out and replaced by technical support. The item in the picture looks like a Metal Oxide Varister (MOV) but I am not sure what you mean - there is no warranty on it because the MOV is damaged? Could you clarify? And also, who is the one telling you all this? Was it APC/Schneider?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

hello

this tel me APC/Schneider in Russia Moscow.

i have mail:

Просьба ознакомиться  и сообщить клиенту данную информацию:

C1-4661078903

SURT8000xli

QS1235350546

Паянная 0P7641

Вместо терморезистора

устанавлен другой элемент.

На фото обведён красным кругом.

Снимается с гарантии.

(See attached file: 7641.JPG)

Если заказчик согласен на платный ремонт, то необходимо его письменное согласие и мы переведем ИБП в постгарантийный отдел.

Сообщите о принятом решении.

Спасибо.

По  поводу  ремонта  снятого  с  гарантии  ИБП   SURT8000 xli :

стоимость  ремонта  составит 35062  руб с  ндс  ( диагностика  + замена-ремонт  2  плат ) Для  перевода  ИБП  из  гарантии  в  постгарантию  необходимо  иметь  Ваше писменное  согласие Best  regards

They argue that the motherboard 0P7641 discovered after opening here this spare part, circled in red in the picture that should not be there, they claim that it was I soldered it there.

They say that instead there should be another transistor (thermistor) and set clear what. and so they want to remove the warranty and identify the cause of not working for UPS /

I ask that it be and where it came from there.

UPS worked after 2 months of purchase

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

Let me look into this a bit and get back to you tomorrow so I can discuss with our EMEA support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

thx you ! i will wait!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

hello vitaly the component that you show in the picture is a Termistor. you can see in  the board appear the name of the component  TH701 means "Termistor 701", and this component is a part of the power supply and if this component is damaged the ups can´t turn on.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

We are still investigating here but I have engaged many parties here to reach a resolution as to what occurred. I will report back hopefully early next week vitaliy.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

thx all !!

TH701 means "Termistor 701" its genue part? not fake on board,

he is there and must be soldered on the motherboard

genuine spare part? refuse to guarantee not have the right? wrong in the warranty service APC?

a nice weekend, I'll wait for your messages.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:53 PM

Still working on coming to a solution for you. Hope to have a final update by tomorrow my time (Eastern time here in the US).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:52 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:52 PM

Sorry for the delay. I think someone should be reaching out to you if not already to help you with this further and do the repair.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:52 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:52 PM

Hello Angela N

I recive message from my saller

APC Moscow, agreed to a warranty repair, in the interests of the client)

Thank you for your support.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:52 PM

0 Likes
0
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:13 AM . Last Modified: ‎2024-03-12 11:52 PM

You're very welcome smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore