Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
SURT8000RMXLT-1TF5/PDU/NetShelter AR3100
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:47 AM. Last Modified: 2024-03-0801:59 AM
SURT8000RMXLT-1TF5/PDU/NetShelter AR3100
Hi!
I'm planning to buy the following.
- SURT8000RMXLT-1TF5: APC Step-Down Transformer RM 2U 208V IN 120V OUT; w/5-20 Receptacles
- AR3100: NetShelter rack
- Basic 0U PDU with 24 120V outlets
The PDU will connect to the SURT8000RMXLT-1TF5. 108/120V equipment will connect to the PDU.
The equipment include the following.
- 1 x IBM x3650 server
- 3 x IBM x3550 servers
- 1 xIBM DS3200 drive array
- 2 xCisco WS-C3560G-48PS-S PoE switches
- 1 xCisco 2851-CCME/K9 router
Please suggest a PDU that will work for this setup.
Since the stepdown transformer's output is 5-20R, if the total power required for the IBM/Cisco equipment is over 20A do I have to split them to 2 separate PDU?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:47 AM. Last Modified: 2024-03-0801:59 AM
Danny,
The #1 problem you're going to run into is load balancing. The PDU's themselves are only capable of approximately 3.5kVA.
The other problem you're going to run into is that the PDU's that output NEMA 5-20R's have an input cord (required) of NEMA L5-20P, due to the capacity of the PDU and NEC code.
Therefore it's going to be impossible to get a PDU to attach to that XFMR that is 5-20 in, 5-20 out.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:47 AM. Last Modified: 2024-03-0801:59 AM
Danny,
The #1 problem you're going to run into is load balancing. The PDU's themselves are only capable of approximately 3.5kVA.
The other problem you're going to run into is that the PDU's that output NEMA 5-20R's have an input cord (required) of NEMA L5-20P, due to the capacity of the PDU and NEC code.
Therefore it's going to be impossible to get a PDU to attach to that XFMR that is 5-20 in, 5-20 out.