SURT5000XLI Internal Fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT5000XLI Internal Fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

0 Likes
7
1876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

SURT5000XLI Internal Fault

My SURT5000XLI S/N NS0604008234 was switched off for the Christmas break. When I switched it back on, after a few minutes, the internal fault light came on and the charge LEDs 3 & 4 (Counting from the bottom) came on. Searching the forum I found a similar problem in this post "SURT3000XLI FAULT" which said the error code reffered to a capacitor soft start up fault. Assuming the the code for my UPS is the same as this post do I simply need te replace the two huge capacitors on the main board to fix the problem?
Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

Thanks for your help any way.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

Thanks for getting back so quickly.
The unit is not supplying power at all now but it did for a few minutes after first switching it on. Until then it showed a near full charge on the batteries. All the batteries in the expansion unit measure 105.5V with105V and 104.8V in the UPS itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

so does the UPS start in bypass at least or is not outputting power at all? is it possible to use a voltmeter to check the battery voltage? i am wondering if the batteries discharged a lot while the UPS was turned off. for the future, when you turn off the UPS, you should disconnect any batteries, especially on these models, to have them avoid discharging into the unit while turned off.

let's measure that batt voltage if at all possible and if that is below a certain amount then that may be the issue here. you can measure each string and see what you get.

this is technically a Battery Capacitor Soft Start Fault.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

0 Likes
1
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

hmm ok those should be good. when you arent working on this, i'd recommend leaving them disconnected to avoid any damage to them while the UPS is not operating correctly.

what i would try is a braindead on the UPS to see if we get anywhere. we need to cut any power to the UPS and remove it from AC power. if possible, you can just trip the input circuit breaker on the back of the unit near the input plug/hardwire connection if it has one, which i think it does. then, make sure all external battery units are unattached and the UPS batteries are and then hold down the off (o) button for 5-10 seconds and see if you hear a click and see some LEDs flash. then reconnect the batteries and put the breaker back to the normal position and see if the UPS starts when you press the on/test button for a second.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

With the input power removed, pressing the off button causes a click sound and the fan to stop rotating. I connected the external batteries and reapplied input power and the fault light immediately comes on. Pressing the off button causes the fault light to go off and there is a click noise but after 5 seconds the fault light comes back on by itself. Pressing the on button does not produce any obvious results.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

ok, well with that, i'd have to say there is an internal issue with the UPS. we have done what we could and like i said, i'd leave your batteries fully disconnected - from the UPS and also the external battery pack so you can use them elsewhere or with a replacement unit.

we dont repair these at all so i'd have to recommend replacing the UPS or trying to figure it out at your own risk. we also don't provide schematics for this type of UPS (or any for that matter). if it is under warranty, you can get a warranty replacement by contacting tech support in your region.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

0 Likes
0
1876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:22 AM . Last Modified: ‎2024-03-11 02:41 AM

Thanks for your help any way.

Reply

Link copied. Please paste this link to share this article on your social media post.

TienAnh
TienAnh
Cadet

Posted: ‎2025-06-15 07:15 PM

In response to BillP
0 Likes
0
586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-15 07:15 PM

Hello. 
I have a SURT5000XLI ups. And its Status is UPS Communication Lost.
I tried to connect to my ups via the RJ45 port on the AP9619 but could not find the IP on my local network.
I also tried to connect to the UPS using the Serial port but its status is UPS Communication Lost.Z
What should we do to fix it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore