SUA 2220 -- Tech had me adjust something in terminal, but what?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA 2220 -- Tech had me adjust something in terminal, but what?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:27 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

0 Likes
8
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:27 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

SUA 2220 -- Tech had me adjust something in terminal, but what?

I have a SUA 2200 and we recently replaced the batteries in it. In PowerChute Business Edition (no network management card here) reported the runtime as 13 minutes, which seemed low. I came on site and checked the battery connections which seemed fine.

I called APC and they had me perform a procedure that the tech admitted he couldn't explain. He only said that the engineer told him to do it.

We used PuTTY to make a serial port connection. From there, he put me in PROG mode. He then had me tap SHIFT-+ (on the number pad) until I saw B3.

Once done, PCBE showed a runtime of 45 minutes.

But I really don't know what he did. In my reading of articles like [this one|http://www.apcmedia.com/salestools/ASTE-6Z8LB2_R0_EN.pdf] it seems we adjusted the number of battery packs in the unit. But that article would seem to indicate this is an adjustment for EXTERNAL battery packs. (I assume external does not refer to the two battery packs I installed INSIDE the 2200.) Plus, the commands don't line up properly.

Basically, I don't have a lot of confidence in that 45 minute number.

FWIW, the load on the unit is 35%.

Any light that can be shed?

Cheers,

m

Message was edited by: mwhalen

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:31 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:31 AM

Thank you. We're all set!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

When you say a "full calibration," are you talking about the battery calibration listed in the Diagnostics page of PCBE?

Is one or the other ("full calibration" vs. pulling the plug) preferable? (I can easily start a calibration remotely, presuming it's done from PCBE. Otherwise, I'll need to go on-site.)

How did you determine what they did? Is there some documentation on what I changed?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

The UPS will recalculate its remaining runtime after a minute or two on battery and will be more accurate than the figure reported by PowerChute while the UPS is online.
I just thought of another question:

What do you mean by that statement above? Is there somewhere OTHER THAN PCBE where I can check the runtime? You seem to be suggesting that the recalculated runtime does not get reported in PCBE during or after the test..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

You should be checking PCBE. What I meant was, when the UPS is running on battery (and has been for a moment or two), the remaining runtime reported by PCBE will probably be more accurate than the remaining runtime reported by PCBE while the UPS is online.

Everytime the UPS goes on battery it will recalculate its runtime based on how quickly it is discharging. When the UPS is online, it is just displaying a number that it believes is the runtime based on how it has been performing during previous transfers to battery.
I see. So, can I do this with the calibration run from PCBE?

Also: where did you get the information regarding adjusting runtime manually?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

If you're looking to do a full calibration (battery will fully discharge), this can be done through the PowerChute interface. Optionally, you could just pull the plug yourself to remove power and let the UPS shut off.
Thanks. I ran one via the PCBE interface this morning. Seems we're only getting a 30 minute runtime. Sucks. Doesn't sound like there's anything more I can do.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

how new is the battery?
Supposedly new. Bought and installed last week.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:32 AM

Assuming you let it charge for 24 hours before doing the test and your load is not fluctuating while on battery (if your load goes up it will decrease runtime) then you should get right around the estimate, within 5 minutes or so, since it was altered to display the correct value for a fresh battery.

If its an APC battery there should be a serial on it - if the battery is old for some reason that may cause diminished runtime. The serial number would help determine that.
It is an APC battery and there is a serial. I don't have it, of course. That information is on-site! ๐Ÿ˜‰

I had given the serial to the tech at APC. He didn't mention whether there were any issues around that, but I didn't ask, "Hey! Is my battery new????"

Yes, I had let it charge for 24 hours.

I suppose the question is:

Considering a constant 35% load on a SmartUPS 2200, would you expect a 35 minute battery run-time?

m

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:31 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:31 AM

At a 35% load (~690 watts) the runtime chart shows 34.6 minutes.
Well, that's nearly dead-on.

I'll mull this over, but I think that really answers my question overall.

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:31 AM

0 Likes
0
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:28 AM . Last Modified: โ€Ž2024-03-13 05:31 AM

Thank you. We're all set!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of