Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Cannot access PowerChute configuration after install on Solaris 11

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cannot access PowerChute configuration after install on Solaris 11
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
9
4309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Cannot access PowerChute configuration after install on Solaris 11

I've installed PowerChute 4.1 on my Solaris 11.3 server (using the PowerChute Network Shutdown v4.1 for Solaris SPARC x64 package).  The installation says it completes successfully, but I cannot access the PowerChute URL, as my browser reports connection refused.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • PowerChute
  • solaris
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

0 Likes
0
4307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

Hi,

Thanks for the update. I have updated the Kbase to reflect the new information.

Thanks again,

Bill

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
4307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Hi,

please attach a copy of the error.log file for review. If installed to the default path you will find the error.log file in 

/opt/APC/PowerChute/group1 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
4307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Hi Bill,

I've attached the error.log file.  

Attachments
error.log
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
4307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Hi,

Please follow the step in Kbase FA276327 and let me know if the issue is resolved. If not after restarting the PowerChute service and attempting to log in attach an update copy of error.log.

The issue you are seeing is caused by a mismatched in available threads compared to the number needed. Below is what I found in error.log

09-12-15 16:57:26,666 FATAL Timer-2 com.apcc.m11.components.WebServer.WebServerThread - Start server exception:
java.lang.IllegalStateException: Insufficient max threads in ThreadPool: max=200 < needed=274

The jar file attached to the Kbase corrects the issue. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
4307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Hi Bill,

Thanks for the response.  

The case that you linked to doesn't seem to be accessible, the link just seems to redirect me to the most recently published FAQs. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:32 AM

0 Likes
0
4307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:32 AM

Hi,

I check the link and it is up now.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:32 AM

0 Likes
0
4307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:32 AM

Yup, the link now works, thanks.

So I have followed the steps and put in the new jar file.  It still does not work, but has a different error message.  I have attached the error log.

Attachments
error.log
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

0 Likes
0
4307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

Hi,

Ok the web service is starting now. The next issue is 

10-12-15 10:32:54,747 FATAL Timer-2 com.apcc.m11.components.WebServer.WebServerThread - Start server exception:
java.io.IOException: Too many open files

PowerChute sets ultimit to 1024  by default in /opt/APC/PowerChute/group1/powerchute.sh

I am thinking to resolve the new issue edit powerchute.sh and change the unlimit -n 1024 to 10000. 

Let me know if this resolve the issue. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

0 Likes
0
4307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

That did it, changing the line in powerchute.sh now allows me to access the web interface.

Thanks for all the help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

0 Likes
0
4308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

Hi,

Thanks for the update. I have updated the Kbase to reflect the new information.

Thanks again,

Bill

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore