SUA 2220 -- Tech had me adjust something in terminal, but what?
I have a SUA 2200 and we recently replaced the batteries in it. In PowerChute Business Edition (no network management card here) reported the runtime as 13 minutes, which seemed low. I came on site and checked the battery connections which seemed fine.
I called APC and they had me perform a procedure that the tech admitted he couldn't explain. He only said that the engineer told him to do it.
We used PuTTY to make a serial port connection. From there, he put me in PROG mode. He then had me tap SHIFT-+ (on the number pad) until I saw B3.
Once done, PCBE showed a runtime of 45 minutes.
But I really don't know what he did. In my reading of articles like [this one|http://www.apcmedia.com/salestools/ASTE-6Z8LB2_R0_EN.pdf] it seems we adjusted the number of battery packs in the unit. But that article would seem to indicate this is an adjustment for EXTERNAL battery packs. (I assume external does not refer to the two battery packs I installed INSIDE the 2200.) Plus, the commands don't line up properly.
Basically, I don't have a lot of confidence in that 45 minute number.
FWIW, the load on the unit is 35%.
Any light that can be shed?
Cheers,
m
Message was edited by: mwhalen
- Labels:
-
Smart-UPS & Symmetra LX | RM
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:31 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:31 AM
Thank you. We're all set!
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
When you say a "full calibration," are you talking about the battery calibration listed in the Diagnostics page of PCBE?
Is one or the other ("full calibration" vs. pulling the plug) preferable? (I can easily start a calibration remotely, presuming it's done from PCBE. Otherwise, I'll need to go on-site.)
How did you determine what they did? Is there some documentation on what I changed?
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
What do you mean by that statement above? Is there somewhere OTHER THAN PCBE where I can check the runtime? You seem to be suggesting that the recalculated runtime does not get reported in PCBE during or after the test..
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
Everytime the UPS goes on battery it will recalculate its runtime based on how quickly it is discharging. When the UPS is online, it is just displaying a number that it believes is the runtime based on how it has been performing during previous transfers to battery.
Also: where did you get the information regarding adjusting runtime manually?
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:32 AM
If its an APC battery there should be a serial on it - if the battery is old for some reason that may cause diminished runtime. The serial number would help determine that.
I had given the serial to the tech at APC. He didn't mention whether there were any issues around that, but I didn't ask, "Hey! Is my battery new????"
Yes, I had let it charge for 24 hours.
I suppose the question is:
Considering a constant 35% load on a SmartUPS 2200, would you expect a 35 minute battery run-time?
m
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:31 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:31 AM
I'll mull this over, but I think that really answers my question overall.
Thank you!
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:31 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:28 AM . Last Modified: 2024-03-13 05:31 AM
Thank you. We're all set!
Link copied. Please paste this link to share this article on your social media post.