SU2200RM3U will not switch to batter power.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU2200RM3U will not switch to batter power.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

0 Likes
3
856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

SU2200RM3U will not switch to batter power.

This unit will not power anything from the batteries. The batteries all have 13V on them out of circuit and appear to be fine. when I press the power button to switch to battery power, whatever is plugged in just goes dead. If I hit the power button with the UPS unplugged from the wall, it comes on lights up and beaps etc, but never sends any power to the outlets even though the batteries appear good. There are two resistors on the board that were toasted up, but still measure good. All the fuses are good.

What components have gone bad??

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

0 Likes
0
856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

This unit will not power anything from the batteries. The batteries all have 13V on them out of circuit and appear to be fine. when I press the power button to switch to battery power, whatever is plugged in just goes dead. If I hit the power button with the UPS unplugged from the wall, it comes on lights up and beaps etc, but never sends any power to the outlets even though the batteries appear good. There are two resistors on the board that were toasted up, but still measure good. All the fuses are good.

What components have gone bad??

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

0 Likes
0
856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

"Is it possible the batteries are bad even though they all measure 13 volts?"

As I explained in the other thread you posted in... Yes.

Also, pressing the button on the front doesn't force it to switch to battery, unless you're pressing & holding the "test" button for 3-4 seconds. Is that what you mean?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

0 Likes
0
856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

Check voltage on battery under load. If they collapse, they're dead. Bad battery will act like a clogged plumbing.

Normal pressure with the faucets closed. Sudden collapse in pressure as soon as something is opened due to inadequate flow.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

0 Likes
0
857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:39 PM . Last Modified: ‎2024-03-14 01:25 AM

This unit will not power anything from the batteries. The batteries all have 13V on them out of circuit and appear to be fine. when I press the power button to switch to battery power, whatever is plugged in just goes dead. If I hit the power button with the UPS unplugged from the wall, it comes on lights up and beaps etc, but never sends any power to the outlets even though the batteries appear good. There are two resistors on the board that were toasted up, but still measure good. All the fuses are good.

What components have gone bad??

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore