bad flash of AP9617

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • bad flash of AP9617
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
lopgok_apc
Crewman lopgok_apc
Crewman

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:27 AM

0 Likes
14
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:27 AM

bad flash of AP9617

I have a apc smart ups 1000. I got a AP9617 from a friend who said they did a bad flash of it.
I read http://forums.isxusergroups.com/thread.jspa?messageID=18717

I brain-deaded the smart ups 1000.
I inserted the card.
I tried to talk via the serial line with hyperterminal.
I got no response whatsoever from hypteterminal.
I had the baud rate, start and stop bits set correctly.

I am using a 940-0024C cable which I know is good because I was able to run
the apc power chute business edition (the web based one) before I inserted the AP9617,
and I could communicate with the ups.
I disabled the apc service before starting hyperterminal.

I also tried the reset button on the AP9617, and pressed it for several seconds.

Is there any way to recover the AP9617 card?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

Assumed answered due to lack of customer update/response.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

can you confirm the port settings in hyperterminal you're using? also, what are the status and link LEDs look like on the card itself when it is inside of the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

lopgok_apc
Crewman lopgok_apc
Crewman

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

Both led's are on, yellow and green, not blinking.

As for hyperterminal, it is COM1 port settings: 2400, 8, none, 1, none

Reply

Link copied. Please paste this link to share this article on your social media post.

lopgok_apc
Crewman lopgok_apc
Crewman

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

Link is yellow.
Status is green.
I do have other com ports, however power chute is working with com1 and that is the com port
that I have the serial cable plugged into.

I will brain dead the unit, and see if I can use hyperterminal now.

Reply

Link copied. Please paste this link to share this article on your social media post.

lopgok_apc
Crewman lopgok_apc
Crewman

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

I typed shift-y and got SM as a response.
I plugged in the ap9617, and pressed lots of enters.
I got a few NA, and then nothing at all.
No replied at all.

The yellow and green led are on, no blinking.
Is there any way to re-flash the card?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

ok so we know your serial connection is working correctly. upon doing a shift Y, and receiving an SM response, i would install the card to the UPS, wait for it to power up and after a minute or two, slide the AP9617 and keep pressing enter after waiting for it to power up completely. if you don't get anything, after doing that, the card may not be recoverable even though it displays good LED indicators 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

sorry! i think I mis-typed.

create a terminal session with the UPS and make sure that you get an SM response from Shift Y. after seeing that, slide in the AP9617 NMC while the UPS is still on. start pressing enter continuously immediately after putting the NMC inside of the UPS. watch the status LED on it to make sure it starts flashing rapidly, alternating between yellow and green. after that stops and the status LED stays solid green or whatever its doing,

if you get any prompts at any point, try to login. if not, then I'd have to say there is an issue here with the card. you COULD try a different UPS incase its a flaky communication problem but I am not so sure that will work - worth a shot though i guess.

Reply

Link copied. Please paste this link to share this article on your social media post.

lopgok_apc
Crewman lopgok_apc
Crewman

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

I have tried all the baud rates, 2400, 9600, 19.2 and 38.4
I hit enter a bunch of times.
Nothing at all.

Is the unit 100% trash?
Would there be any point to removing the button cell battery?
Is there no way to recover from a bad flash?

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:37 PM . Last Modified: β€Ž2024-03-14 01:26 AM

the only thing actually that just came to mind is to make sure you try different baud rates. the UPS communicates at 2400 but someone may have changed the baud rate on the management card itself.

try 9600, 19200, and 38400, keeping the rest of the settings the same and see if you get anything after tapping enter a bunch of times at each speed.

this info/instructions are listed here about the baud rates.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

there must be something wrong with the card here..there is really nothing else i can think of trying unfortunately 😞

the only thing actually that just came to mind is to make sure you try different baud rates. the UPS communicates at 2400 but someone may have changed the baud rate on the management card itself.

try 9600, 19200, and 38400, keeping the rest of the settings the same and see if you get anything after tapping enter a bunch of times at each speed.

this info/instructions are listed here about the baud rates.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

on this particular card, you have gone through all of the tips/tricks i can think of to try and recover the firmware on the card. there may be something else going on here other than a bad flash. the coin cell battery keeps the date on the time on the card and thats it so its up to you what you want to do with it.

i cant think of anything else to do here if the card isnt working besides getting a new one πŸ˜•

Reply

Link copied. Please paste this link to share this article on your social media post.

lopgok_apc
Crewman lopgok_apc
Crewman

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

I have a apc smart ups 1000. I got a AP9617 from a friend who said they did a bad flash of it.
I read http://forums.isxusergroups.com/thread.jspa?messageID=18717

I brain-deaded the smart ups 1000.
I inserted the card.
I tried to talk via the serial line with hyperterminal.
I got no response whatsoever from hypteterminal.
I had the baud rate, start and stop bits set correctly.

I am using a 940-0024C cable which I know is good because I was able to run
the apc power chute business edition (the web based one) before I inserted the AP9617,
and I could communicate with the ups.
I disabled the apc service before starting hyperterminal.

I also tried the reset button on the AP9617, and pressed it for several seconds.

Is there any way to recover the AP9617 card?

Reply

Link copied. Please paste this link to share this article on your social media post.

lopgok_apc
Crewman lopgok_apc
Crewman

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

When I type shift y, I get a response of SM
When I type shift a, I get a beep, and a response of OK
I can't easily see the leds right now.
When I hit return, I get a reply of NA

Message was edited by: lopgok

Reply

Link copied. Please paste this link to share this article on your social media post.

lopgok_apc
Crewman lopgok_apc
Crewman

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

I am not sure what you mean by slide the card.
Please clarify.

Message was edited by: lopgok

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

0 Likes
0
2388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:38 PM . Last Modified: β€Ž2024-03-14 01:26 AM

Assumed answered due to lack of customer update/response.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore