Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

SU2200INET and linux?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: SU2200INET and linux?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
pavelp_apc
pavelp_apc
Cadet

Posted: ‎2021-07-07 11:44 PM

0 Likes
7
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 11:44 PM

SU2200INET and linux?

This was originally posted on APC forums on 11/11/2017


Hello,
I just got an used APC Smart-UPS 2200 ( SU2200INET ) that came without the cables. I noticed that it has a Serial port in the top right corner and the extra "Basic Monitoring Port" ( AP 9607 ).
Q1: Are those ( http://www.apc.com/shop/bg/en/products/APC-Smart-UPS-2200VA-230V/P-SU2200INET ) the only available guides for that device ?
Based on the guides above, I understand that the black serial port in the top right corner is the "Advanced Monitoring Port" and I can use it to collect information about the state of the device. I also understood that APC uses proprietary mapping, so I need to use special serial cable.
If I got the things above right, my question is can I connect the SU2200INET using APC 940-0024 serial cable in order to monitor the device via the serial port of a machine running linux? Is this my best approach? What software could I use?
Can someone share some experience with this device and linux? Thanks!
Regards,
Pavel
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-07-07 11:44 PM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 11:44 PM

This was originally posted on APC forums on 1/14/2018


A cheaper alternative to the card is the serial cable and NUT which integrates well with any flavour of Linux.  You can pick up the cables on eBay or make your own.

See Answer In Context

Reply
Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:44 PM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 11:44 PM

This reply was originally posted by Gareth on APC forums on 11/11/2017


Personally you cannot beat the network management cards for the APC UPS, you can pick them up cheap enough on eBay.

Reply
pavelp_apc
pavelp_apc
Cadet

Posted: ‎2021-07-07 11:44 PM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 11:44 PM

This was originally posted on APC forums on 11/11/2017


Hello,
Thank you. Do you mean AP9606 or some other device ?
Regards,
Pavel

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:44 PM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 11:44 PM

This reply was originally posted by Gareth on APC forums on 11/12/2017


If it says that is the one for your UPS then yes.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:44 PM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 11:44 PM

This reply was originally posted by Bill on APC forums on 11/13/2017


Hi,

It would be helpful to know what version of Linux you are running to make the proper recommendation. 

As for the AP9606 unless you only what to access the UPS over the Internet I do not recommend that card. If you are looking for a card that is compatible with PowerChute Network Shutdown or if you plan to run APCUPSD using PCNET you should find a AP9617 at a minimum. 

Reply
pavelp_apc
pavelp_apc
Cadet

Posted: ‎2021-07-07 11:44 PM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 11:44 PM

This was originally posted on APC forums on 1/11/2018


Hello Bill,

Thank you for the good reply and really sorry for missing to come back! I somehow deleted the email notification for the thread.
Currently I run CentOS6 as host os/ plan to move to debian/ubuntu at some point/, VM guest running debian9/ubuntu16 and OpenWRT / plan to move to lede/ . So if I go for network card I should be okay. If i go for serial cable, I need to stay compatible with CentOS6 running linux kernel 2... 


I would be interested to get out of the APC device 
- Device Health - are batteries okay, are there errors etc. I'm not visiting the room often.
- Event information / trigger over the internal network - somehow to catch an event when the device is below 30% for example, so I should initiate shut down of my boxes...

Looking forward to your advice on what card or cable may be beneficial to look for.

Regards,
Pavel

Reply
Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-07-07 11:44 PM

0 Likes
0
645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 11:44 PM

This was originally posted on APC forums on 1/14/2018


A cheaper alternative to the card is the serial cable and NUT which integrates well with any flavour of Linux.  You can pick up the cables on eBay or make your own.

Reply
intelligent002
intelligent002
Cadet

Posted: ‎2023-02-22 01:45 PM

0 Likes
0
188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2023-02-22 01:45 PM

hey guys,

 

i've got the same old good SU2200INET model, and i'm freaking out with the serial cable pinout. cannot find the one that will allow getting the info from the unit.

 

tried to make my own, made the 940-0024C by this diagram https://alioth-lists.debian.net/pipermail/nut-upsuser/2005-August/000118.html - and 940-1524D by that diagram https://pinoutguide.com/UPS/apc_smart_cable_pinout.shtml

no luck with both.

 

does anybody got the right pinout for SU2200INET ?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc